Can I run a ground wire from one out let to the next. (3 outlets total )
Then to a grounding rod that's outside
|
|
 |
Uber Member
|
|
May 2, 2011, 01:46 PM
|
|
Are there no ground wires to start? Is this a metal box? Have you checked to see if a ground exists at the first outlet? Measure voltage between a black and the metal box. What do you get? 120VAC? Then you have a ground. Older outlets had no ground and a ground was run to the box unless this is very old knob and tube. Please explain why you need or think you need a ground rod.
|
|
 |
Home Repair & Remodeling Expert
|
|
May 2, 2011, 01:46 PM
|
|
Are you attempting to make a two prong receptacle into a 3 prong?
|
|
 |
New Member
|
|
May 2, 2011, 05:58 PM
|
|
No ground to start -- 2 wire aluminum not metal box - no exsisting ground that I'm aware of . I just bought this house the inspector is telling me the outlets are not grounded I'm remodeling and do not want to open walls later - safety reasons I guess have a baby or is it not a big deal - idid have a new 200 amp panel installed everythimg works fine - but it was brought up in the inspection report
|
|
 |
New Member
|
|
May 2, 2011, 06:02 PM
|
|
Just trying to make my house safe and am spending lots of money remodeling
Want to cover all the insade the wall issues now
|
|
 |
Home Repair & Remodeling Expert
|
|
May 2, 2011, 06:08 PM
|
|
TK or one of the electricians can tell us the code but I am sure the ground wire must be inside the same cable or conduit as the hot and neutral back to the panel. You can make your outlets into 3 prong by replacing the receptacles with GFCI receptacle, however they won't be truly grounded but will be ground faulted. Bedrooms in new or significantly remodeled homes need ARC fault receptacles. Is this a pre-closing home inspection or is it the city building inspector talking to you about your remodel. Do you know about alumium wire and how connections must be done?
|
|
 |
Home Repair & Remodeling Expert
|
|
May 2, 2011, 06:09 PM
|
|
Do not start a new thread with each question, it just confuses us old folks. Put you reply in the box at the bottm of your other older post.
|
|
 |
Printers & Electronics Expert
|
|
May 2, 2011, 06:25 PM
|
|
Ballengerb1 is correct.
The equipment grounding conductor has to originate at the main service panel or a secondary panelboard.
The entire circuit would have to be re-run from the panelboard with 14/2 or 12/2 depending on what the amperage of the circuit is.
14/2 is used for 15 amp and 12/2 is used for 20 amp.
The alternative that Bob is speaking of is to use a GFCI receptacle. That would give ground fault protection. The receptacle would have to be labeled as ungrounded.
If you need the code citation, I will be happy to get it for you.
|
|
 |
Home Improvement & Construction Expert
|
|
May 3, 2011, 04:10 AM
|
|
no ground to start -- 2 wire aluminum not metal box
If you have aluminum wire and are remodeling, pull out the old stuff and rewire.
PS
Find a few periods and capital letters for your post.
|
|
 |
New Member
|
|
May 10, 2011, 11:27 PM
|
|
An updated service panel isn't really going to do you much good with outdated, ungrounded branch circuits
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
How do I run a ground wire to a light switch?
[ 4 Answers ]
I have the 'old' light switches that do not require a ground wire to work, all of the switches are connected to a control box on the attic. I want to install new switches, but all of the new switches require a ground to work? All of these switches are connected in series, the reason I know this, is...
Need to run a wire from 50 amp circuit breaker to outside outlets
[ 4 Answers ]
My band is performing outside. We have several pieces of equipment that need power. However, we are about 120 feet from the power source where there is a breaker box and 1 outlet. I've been told that this is a 50 amp circuit.
I need several outlets to plug in all our gear. I need to know the...
View more questions
Search
|