    100 Amp Service to Barn?
    I am confused on the proper ground and bonding here is what I have: 100 amp disconnect coming off Meter (2 hot, 1 common), then 4 wires to the 100 amp panel in barn (2 hot, 1 commmon, and 1 ground). My question is do I bond this ground to the common at the disconnect and then connect to the added equipment ground at the panel and do not pput in the bond screw? I have ground rod at the panel connected to equipemnt ground in the barn.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Apr 11, 2011, 09:30 AM
    See if you can follow the diagram below I found at DIYchatroom.com:
    Attached Images
     
    ekwalker's Avatar
    ekwalker Posts: 3, Reputation: 1
    New Member
     
    #3

    Apr 11, 2011, 10:30 AM
    Ok, IF I am reading that correctly, bond at the Disconnect and do not bond the equipment and common at the panel in the barn. Am I correct or way off? I have asked some local electricians and each have a different opinion, I guess that is why I am so confused.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Apr 11, 2011, 10:39 AM
    You are 100% correct, the neutral and equipment ground cannot be connected at any place but the Main.

    Only deal with the electricians that told you what I have told you.
    ekwalker's Avatar
    ekwalker Posts: 3, Reputation: 1
    New Member
     
    #5

    Apr 11, 2011, 11:14 AM
    1 said to do it that way and another said to not even run the ground wire between the disconnect and the panel at the barn.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Apr 12, 2011, 02:31 AM
    Hire the one electrician that explained to do it as the diagram.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Service entrance cable size for 100 amp and 200 amp service. [ 16 Answers ]

I would like to know what size aluminum sec I would need for 100 or 200 amp service

Overhead from a 100 amp service panel to a 100 amp subpanel in a garage. [ 6 Answers ]

An Electrician friend said I could use #4 copper for the (2)120 volt legs and a conventional Suspension wire as the nuetral. The overhead span is about 35 feet and the overall run From panel to panel is about 70 feet.The supply outlet said to use #2 copper. Also, what type wire for sunlight...

How much does it cost to change 100 amp service to 200 amp service? [ 5 Answers ]

I am buying a house with 100amp service and the home inspecter said I would need at least 150 amp panel to service the hot tub that comes with the home. However, the hot tub is hooked up to the 100amp service panel and the hot tub works fine. Am I really running into any issues here if I do...

100 amp main, 100 amp service wire, 200 amp sub panel? [ 2 Answers ]

I am moving my sub panel and upgrading to a 200 amp service, but in phases. The first phase is to move the panel due to some remodeling. I want to put a 200 amp panel in the laundry room with a 200 amp breaker. I have 100 amp feeder wire going to it (AL 2/2/2). Outside I have the meter can and...

100 amp service to my pole barn [ 1 Answers ]

I am installing a 100 amp service in my pole barn. It is 250 feet from the house panel. What size wire and conduit do I need to bury for that distance? Thank you


View more questions Search