    I have an underground (10-2) wire and was wondering if it is acceptable to run that to a sub-panel (in a shed) supplied by a 30amp 2-pole braker with the black and white hot and the ground as neutral, then drive a grounding rod at the sub-panel for ground/neutral bonding
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Nov 29, 2010, 09:15 AM

    No!

    A sub-panel requires a four wire feeder, per NEC.

    You will also have to keep ground and neutral isolated from each other. The bonding jumper cannot be installed in the sub-panel.

    Also, since the building is a separate structure, you must set at least on ground rod and connect the sub-panel to this rod via a grounding electrode conductor.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Grounding [ 2 Answers ]

If my Home's Breaker Panel is not grounded, does my Meter Panel have to be? This may sound stupid, but I did not see any grounding on my Home's Breaker Panel or the Meter Panel outside on the pole. Is this possible, that neither is grounded? Wouldn't the whole wiring system not work properly in...

Grounding [ 0 Answers ]

What is the difference between grounding,earthing and neutral

Grounding an outlet with a grounding pigtail [ 5 Answers ]

I was helping a friend replace outlets in his old house. The original outlets have two wires and no ground. They are mounted in a metal box. We installed the new 3 pronge outlets and used grounding pigtails to ground them to the metal box. We turned the power back on after completion and none...

Grounding and outlet [ 4 Answers ]

If the outlet box is grounded does the outlet have to be grounded

Differnce between neutral grounding and separated grounding [ 1 Answers ]

What is the difference between neutral and separate grounding?? Why and when do you defer between them?? Basically why do we ground, what's its purpose and what are the differences between the varying methods. I hope I don't sound dumb but the US NAVY nuclear electrical school didn't teach me ...