    Generator back feeding
    I am running 220 volt 50 amp service from my house to my garage where there will be a receptical. I have a 50 amp breaker I nserted into the fuse box with 6-3 wire. The wire has 2 hot and a alumimum grounc. Now my generator ia a 5000 watt 41.7 amp single phase generator. How do I connect the wireing to backfeed from the generator through the 220 volt 50 amp receptical to power my house? Oviously the main breaker is off when generator is in use
    Fr_Chuck's Avatar
    Fr_Chuck Posts: 81,301, Reputation: 7692
    Expert
     
    #2

    Oct 28, 2010, 06:45 PM

    Well actually the breaker is not known to be off for sure, or turned on by accident unless of course you use the proper system to connect with a auto shut off.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Oct 29, 2010, 02:46 AM
    What is being proposed is not allowed. There must be either a manual or automatic transfer switch, or an interlocking device, that will mechanically insure the utility circuit breaker or line is open while the generator feed is energized.

    Cannot rely on a human to insure the utility circuit breaker is open.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Pros/Cons of Breast feeding vs. Formula feeding. [ 9 Answers ]

I have heard that if you don't breast feed your baby will have an unhealthy immune system (although I am pretty healthy, and was bottle fed), and I have also heard horror sotries about breast feeding. What are good vs. bad of breast feeding/bottle feeding?:D:D

Connecting a back up generator to residence power [ 0 Answers ]

I have to connect a back up generator to a small printing business. A 4 Kw gen is suffice as I have done a load test. I want to know if I can connect it by taking the utility power through a break before make Isolator back to the distribution board that feeds the building. Secondly, they are using...

Back fire when starting jiangdong chinese petrol generator [ 0 Answers ]

When I try to start my gen with electric self starter it hiccups. When I try it manually it back fires but starts after a few attempts. When I shut it off it stops with back fires. Some problem with timing I think but it does not have an adjuster as in motor bikes. Need help

I require for a Power Plus 5000 Generator 1 generator under following specifications: [ 1 Answers ]

I require for a Power Plus 5000 Generator 1 generator under following specifications: 5000 Watts, 120V, 1 Phase, 60 Hz at 3600 RPM, 3720 RPM at no-load. Thank you, Publio

Back-up generator connections [ 5 Answers ]

I have a 3 yr old - 2 stage American Standard gas furnace. I tried to use a generator in an emergency, by disconnecting the hard wiring from the switch next to the furnace - and putting a good, 3 prong pigtail on the wires coming from the furnace. All I got was clicking and a sound like it was...


View more questions Search