    Generator back feeding
    I am running 220 volt 50 amp service from my house to my garage where there will be a receptical. I have a 50 amp breaker I nserted into the fuse box with 6-3 wire. The wire has 2 hot and a alumimum grounc. Now my generator ia a 5000 watt 41.7 amp single phase generator. How do I connect the wireing to backfeed from the generator through the 220 volt 50 amp receptical to power my house? Oviously the main breaker is off when generator is in use
  • Oct 28, 2010, 06:45 PM
    Fr_Chuck

    Well actually the breaker is not known to be off for sure, or turned on by accident unless of course you use the proper system to connect with a auto shut off.
  • Oct 29, 2010, 02:46 AM
    tkrussell
    What is being proposed is not allowed. There must be either a manual or automatic transfer switch, or an interlocking device, that will mechanically insure the utility circuit breaker or line is open while the generator feed is energized.

    Cannot rely on a human to insure the utility circuit breaker is open.