[ 8 Answers ]
I am looking for confirmation on some of the info I have found and answers to a few missing pieces. This is regarding wire size and conduit size for service conductors from the meter to the breaker panel (about 30 ft away). Wire Size: 125A service needs #2 copper or 1/0 aluminum -- #6 copper...
Issues when replacing single circuit breaker with duplex breaker
[ 3 Answers ]
I have a Westinghouse B20 2040CT Circuit Breaker Panel with a 200 amp main. I am remodeling my kitchen and would like to correct some of the current wiring problems I inherited when I purchased the house. A number of circuits are current heavily loaded and I want to take this opportunity to...
Can we convert the 220v breaker in to 24v breaker(vaccum ckt bkr).how
[ 1 Answers ]
Can we convert the 220v vacuum ckt bkr in to 24v vcb? How. Can u explain. Can we use differential relay bkrs in the place of 24v bkr?
Electrical nfpa 70 sizing of ac equipment wire and breaker size
[ 2 Answers ]
Ac equipment. Minimum circuit ampacity is 18 amps max is 40. What size wire and what size breaker? View more questions Search
|