    200 amp service
    A Carroll EMC employee says that the 200 amp main breaker on the breaker box protects either phase [120 v] at 200 amps. I conclude, therefore, that the total available amperage at 120v is 400, assuming no 240v circuits are wired. Is my assumption correct, and/or is the CEMC employee correct?

    I had always assumed that the total amperage was 200 and that the main breaker would throw if total amperage reached some high percentage of 200.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Apr 10, 2010, 07:52 AM

    This can be confusing. A 200A residential service is 200A @ 240v. You can say this is equivalent to 400A @ 120v, but this is not really accurate.

    Bottom line is this service will deliver 48,000 watts worth of power.

    You are correct in that the main will trip if either leg of the service (or both) reach somewhere well over 200A. Breaker do not trip as soon as they exceed their rating. There is quite a trip curve.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Service entrance cable size for 100 amp and 200 amp service. [ 16 Answers ]

I would like to know what size aluminum sec I would need for 100 or 200 amp service

Running 100 amp service panal 200 ft away from main 200 amp service [ 4 Answers ]

I am looking to find out how big the wire needs to be to carry the load. This will be a 100 amp service coming from a 200 amp main . It will need to travel 200 to 250 ft underground to a barn. If some one could help me that would be great thaxs)))

Relocating and upgrading my 200 amp service to 400 amp service [ 4 Answers ]

Im getting ready to upgrade and relocate my 200 amp service to a 400 amp service about 10 feet away away from original location. A new 400 amp meter base will be back to back with 2 new 200 amp panels. My question is, can I take out the guts out of my 200 amp panel and use it as a junction box to...

Extending 200 amp service to another 200 amp panel [ 1 Answers ]

Hello Everyone, As I just found this site this is my first time posting. I am in the process of doing an addition to my home and I am having the electrical service moved as the addition is on an exterior wall. I installed a new 200 amp panel and I need to extend the electrical over to my...

200 amp service with a 200 amp outdoor breaker [ 1 Answers ]

I need to know how to wire a 200 amp outdoor breaker enclosure.I have 4/0 scu cable for my service head to the meter,and 4/0 scu from meter to breaker enclosure.Then from the breaker enclosure I have 4/0 ser cable to my panel.What is the proper wiring method in the enclosure,please help.


View more questions Search