    antoniarocks Posts: 3, Reputation: 1
    New Member
     
    #1

    Mar 23, 2010, 10:57 AM
    Troubleshooting challenge - furnace runs then ignition proving failure
    I have a 10 year old Bryant 395CAV furnace. It starts and runs fine... after the temp has gone up between 1-2 degrees, it shuts off with error code 34 (Ignition Proving Failure). If I wait a few minutes and then turn power off and then on, it will start and run fine and then will shut off again with error code 34.

    What is strange in this case is the combination of the furnace running for a while and the error code 34 (Ignition Proving Failure). From what I've been told, most of the Ignition Proving Failure problems would cause the furnace to not run at all.


    I have (or plumber) done the following and the problem persists:
    Cleaned filter
    Replaced thermostat
    Cleaned flame sensor with steel wool
    Replaced flame sensor
    Tested the ignitor
    Tested the gas valve
    Tested the electrical wires with a voltmeter
    Replaced the control board

    Fyi all the burners light and run until code 34

    Any idea what is going on here?
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #2

    Mar 23, 2010, 11:21 AM

    I would say you need a control board, but that has been changed? Was it the exact board or a universal? Next thing to check would be a pressure switch on the vent if equipped.
    antoniarocks's Avatar
    antoniarocks Posts: 3, Reputation: 1
    New Member
     
    #3

    Mar 23, 2010, 01:06 PM

    It was the exact board... not sure about a pressure switch on vent... I can check on that.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #4

    Mar 24, 2010, 06:09 AM

    Try this: raise thermostat setpoint to demand heating, and wait for burners to ignite. Wiggle the wires connected to the gas control. If main burners drop out, the terminal block interface on the gas control is failing.
    antoniarocks's Avatar
    antoniarocks Posts: 3, Reputation: 1
    New Member
     
    #5

    Mar 24, 2010, 12:17 PM

    Thanks KC... tried this... nothing happened, the burners did not drop out.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #6

    Mar 24, 2010, 12:26 PM

    Is there a green wire connected between the gas control & the gas manifold? It is usually found where the manifold is attached to the mounting bracket.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Ignition Proving Failure Bryant 383KAV [ 15 Answers ]

Ignition Proving Failure - Bryant 383KAV042091 AGJA, series G 88BTU/HR, 80% AFUE Ran fine all last season. Power stayed on through the summer with thermostat on lowest setting. When turned on this season - no heat. I would very much appreciate help with diagnosing this problem. I have read a...

Another bird in the vent? (Ignition Proving Failure) [ 18 Answers ]

Several days ago my gas furnace quit working unexpectedly during the night without any warning signs. It is a Carrier 58MXA100-16 manufactured in 2005, in service since 2007. I get status code 34 “Ignition Proving Failure”. Steps I went through in troubleshooting: 1. Turn heat on at...

Ignition failure [ 28 Answers ]

My Goodman furnace shows a one blink code that translates to ignition failure and suggests checking the flame sensor (which I replaced) the gas valve (which I replaced) gas pressure (had new gas meter installed) or restricted gas flow (which I can't imagine) Any help is greatly appreciated.

Ignition failure carrier furnace [ 1 Answers ]

Thk for the reply, I tried connecting a wire from the spark generator post and holding the other end 1/8 inch from the ground. First try a got a short burst of 3 weak sparks. Shut off furnace and re started this time no sparks a all. Checked that there was still voltage going to the SG unit. Guess...

Ignition proving failure [ 12 Answers ]

Carrier model 58RAV. Once a month the heating system's led code shows 14 ignition proving failure,after a couple of hours it resets itself and everything is fine.What gives?


View more questions Search