    Troubleshooting challenge - furnace runs then ignition proving failure
    I have a 10 year old Bryant 395CAV furnace. It starts and runs fine... after the temp has gone up between 1-2 degrees, it shuts off with error code 34 (Ignition Proving Failure). If I wait a few minutes and then turn power off and then on, it will start and run fine and then will shut off again with error code 34.

    What is strange in this case is the combination of the furnace running for a while and the error code 34 (Ignition Proving Failure). From what I've been told, most of the Ignition Proving Failure problems would cause the furnace to not run at all.


    I have (or plumber) done the following and the problem persists:
    Cleaned filter
    Replaced thermostat
    Cleaned flame sensor with steel wool
    Replaced flame sensor
    Tested the ignitor
    Tested the gas valve
    Tested the electrical wires with a voltmeter
    Replaced the control board

    Fyi all the burners light and run until code 34

    Any idea what is going on here?
  • Mar 23, 2010, 11:21 AM
    Joshdta

    I would say you need a control board, but that has been changed? Was it the exact board or a universal? Next thing to check would be a pressure switch on the vent if equipped.
  • Mar 23, 2010, 01:06 PM
    antoniarocks

    It was the exact board... not sure about a pressure switch on vent... I can check on that.
  • Mar 24, 2010, 06:09 AM
    KC13

    Try this: raise thermostat setpoint to demand heating, and wait for burners to ignite. Wiggle the wires connected to the gas control. If main burners drop out, the terminal block interface on the gas control is failing.
  • Mar 24, 2010, 12:17 PM
    antoniarocks

    Thanks KC... tried this... nothing happened, the burners did not drop out.
  • Mar 24, 2010, 12:26 PM
    KC13

    Is there a green wire connected between the gas control & the gas manifold? It is usually found where the manifold is attached to the mounting bracket.