    Grounding a 200 Amp Service
    I am installing a new 200A load center (main) for a 100A (existing) panel. I noticed that the ground wire is just a 14/2 wire run outside:). I will need to run a ground from the new panel but the water meter is about 25' away. Can I run the new bare copper ground wire through the wall and into the ground outside? What size wire should it be and would a grounding rod be easier to put in or would it be better to use a grounding plate
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Mar 7, 2010, 04:32 AM
    Since you have city water, and I will assume that is is metal pipe, you must run a #4 copper to the point the water line enters the building, jump out the water meter with the same wire, using two pipe clamps for #4 wire. You then must install either a ground rod or plate and either continue with the #4 or run a #6 from the neutral/ground bar in the Main to the rod or plate.

    I have only used rods, more readily available.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Service entrance cable size for 100 amp and 200 amp service. [ 16 Answers ]

I would like to know what size aluminum sec I would need for 100 or 200 amp service

Running 100 amp service panal 200 ft away from main 200 amp service [ 4 Answers ]

I am looking to find out how big the wire needs to be to carry the load. This will be a 100 amp service coming from a 200 amp main . It will need to travel 200 to 250 ft underground to a barn. If some one could help me that would be great thaxs)))

200 amp service / grounding [ 3 Answers ]

I have a 200 amp meter on a power company pole in the country for barn electricity. I have built a small shed 285' away and want 100 amp service. Based on the distance, I am planning on using 4/0 4/0 2/0 Al URD cable in 2" conduit buried 24". To get the lug sizes to fit the 4/0, I am using 200...

Extending 200 amp service to another 200 amp panel [ 1 Answers ]

Hello Everyone, As I just found this site this is my first time posting. I am in the process of doing an addition to my home and I am having the electrical service moved as the addition is on an exterior wall. I installed a new 200 amp panel and I need to extend the electrical over to my...

200 amp service with a 200 amp outdoor breaker [ 1 Answers ]

I need to know how to wire a 200 amp outdoor breaker enclosure.I have 4/0 scu cable for my service head to the meter,and 4/0 scu from meter to breaker enclosure.Then from the breaker enclosure I have 4/0 ser cable to my panel.What is the proper wiring method in the enclosure,please help.


View more questions Search