    200 amp service / grounding
    I have a 200 amp meter on a power company pole in the country for barn electricity. I have built a small shed 285' away and want 100 amp service. Based on the distance, I am planning on using 4/0 4/0 2/0 Al URD cable in 2" conduit buried 24". To get the lug sizes to fit the 4/0, I am using 200 amp breakers and load centers.

    On the electrical pole, just below the meter, I plan to have a 200 amp circuit breaker, then go through the conduit to the shed, where I will have a 200 amp Main Lug Center. I plan to keep the equipment ground separate from neutral all the way back to the circuit breaker panel on the power pole, where I will bond them.

    My questions are:

    1. If I bond the neutral and equipment ground at the circuit breaker on the power pole as described above, what Cu wire size for equipment ground would you recommend based on the distance of 285'?

    2. Can the equipment ground wire be run bare in the same conduit with the 4/0 4/0 2/0 URD cable, or should the ground wire be jacketed?

    3. As an alternate, to save money on the Cu equipment ground wire, can I eliminate the 285' of ground wire altogether by adding a second circuit breaker at the panel at the shed (I want to keep the breaker at the power pole to protect the 285' of buried cable) and bonding the neutral and equipment ground at the shed panel, and having two 8' brass ground rods at the shed? In other words, with grounding and bonding at the breaker panel at the shed, does the application still need to have an equipment ground wire running back to the breaker panel on the power pole?

    Thank you!
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Aug 17, 2007, 05:25 AM
    Grounding the grounded conductor must begin at the first means of disconnect. It is at this point the equipment grounding begins and is separated from the grounded conductor (neutral).

    You can either eliminate the Main Disconnect at the pole, (which I understand you want to use) or use 4 wire URD cable from the disconnect at the pole to the panelboard in the shed.

    Having a second main disconnect at the panel is not required and offers nothing but convenience.

    If you already own the 3 wire URD, then add a #4 copper bare or insulate or # 2 aluminum insulated next to the cable.

    Drive at least one 8 foot ground rod (two is better, and may be required in your area)and connect it to the neutral bar at the main disconnect. The neutral bar at the main will have the input neutral, output neutral, the grounding electrode conductor from the rod, and must also connect to the metal box using a screw driven through the bar into a machine threaded hole, or use a small jumper wire.

    At the panel, the neutral bar must be kept insulated from the metal box and any equipment grounds. The equipment ground bar and any equipment grounding conductors all connect directly to this bar, which is bolted directly to the metal box using machine thread screws and threaded holes.
    Diedre's Avatar
    Diedre Posts: 1, Reputation: 1
    New Member
     
    #3

    Oct 25, 2008, 05:49 PM

    Does no 6 grounding wire 200 amp service have to be insulated or can it be bare going from ground rod to the panel
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Oct 25, 2008, 05:58 PM

    Yes it can be bare.

    Remember, #6 can only be used if going to a ground rod(s).

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Running 100 amp service panal 200 ft away from main 200 amp service [ 4 Answers ]

I am looking to find out how big the wire needs to be to carry the load. This will be a 100 amp service coming from a 200 amp main . It will need to travel 200 to 250 ft underground to a barn. If some one could help me that would be great thaxs)))

400 amp service, 2 200 amp panels, 320 amp meter socket [ 10 Answers ]

Hi, this is my first post here, but I have been reading a lot and have already learned a bunch. I want to thank TK already and hope you reply to this. I am in the process of designing my electrical system for my new home. I have some electrical experience, but am by no means a pro. I am...

400 amp service with 2-200 amp panels & 320 amp socket [ 6 Answers ]

Hi TK. I am running 400 amp service into my new contruction home. The electric compnay is running a single 400 amp line to the meter. I have to split it to the two panels at that point. You had told me once before that I need a 320 amp meter socket and then run 2-200 amp lines to the separate...

100 amp service vs. 200 amp service [ 5 Answers ]

The house I just bought was built in 1952. It's a 3 bedroom, 1 bathroom with the standard screw in fuses (total amps unknown). Presently I'm doing a remodel. Adding a third bedroom & extra bathroom, washer & dryer, dishwasher, newer & larger refrigerator, bigger microwwave, probably 3 window air...

200 amp service with a 200 amp outdoor breaker [ 1 Answers ]

I need to know how to wire a 200 amp outdoor breaker enclosure.I have 4/0 scu cable for my service head to the meter,and 4/0 scu from meter to breaker enclosure.Then from the breaker enclosure I have 4/0 ser cable to my panel.What is the proper wiring method in the enclosure,please help.


View more questions Search