    Can you have a higher main breaker then what your service is
    I currently have a 200 amp service. I ordered a panel which I thought was a QO140M200 and instead received a QO140M225. Will this still work for a 200 amp service? The only reason I'm having the panel changed is because (1) it's a rats nest inside and (2) it's full considering it's only 30 space.. thanks for your input
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Mar 4, 2010, 04:59 PM
    200 Amp service entrance conductors can serve a 225 amp Main Breaker, however, accurate detailed load calculations must be done to show that the conductors are sized properly.

    Better off getting the 200 amp panel, if at all possible.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can I tapinto the line side of a100 amp main breaker to feed a 60 amp breaker service [ 1 Answers ]

Can I tap into the line side of a 100 amp main breaker to feed a 60 amp breaker for a electric stove

Size of main breaker and service entrance cable [ 1 Answers ]

Hi, I am new on this site. I just want to know what is the minimum size of service entrance conductor and main breaker for 17 lighting outlets and 15 conveniece outlets plus one 1.5Hp aircon and 2000 heater. Your reply would be highly appreciated. Thank you.

Load Center Main Lug or Main Breaker for the Attic [ 5 Answers ]

I have a large attic (on 3rd floor), 38'x28', which is unfinished space. The 2nd floor central air-condition is located there and used to be fed by a 60 feet of 12/3 cable (I changed the cable to 10/3 to reduce the chance of voltage drop) and it's fed by a dual 15A breaker (240v breaker) in the...

Replacing Circuit Breaker with Higher AMP Breaker [ 8 Answers ]

Excuse me, I did look at the code book as is suggested in your Sticky. The NFPA may answer this question, but I am not knowledgeable enough to recognize it: Our offices are upstairs in an older (renovated home) building with modern wiring. We have 4 computers, 3 printers, and miscellaneous with...

Can I convert a main breaker Cutler Hammer loadcenter to main lug? [ 1 Answers ]

I was wondering if Cutler Hammer made a part to convert a main breaker load center (CH) style, to a main lug panel. If so, does anyone know the part number or can you refer me to a location where I could find it? Cutler Hammer's website is not too user friendly. Thanks


View more questions Search