  • Mar 4, 2010, 03:13 PM
    give_em_the_blade
    Can you have a higher main breaker then what your service is
    I currently have a 200 amp service. I ordered a panel which I thought was a QO140M200 and instead received a QO140M225. Will this still work for a 200 amp service? The only reason I'm having the panel changed is because (1) it's a rats nest inside and (2) it's full considering it's only 30 space.. thanks for your input
  • Mar 4, 2010, 04:59 PM
    tkrussell
    200 Amp service entrance conductors can serve a 225 amp Main Breaker, however, accurate detailed load calculations must be done to show that the conductors are sized properly.

    Better off getting the 200 amp panel, if at all possible.