    What are typical flue gas results in a AFG
    What are typical flue gas results in a AFG
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Feb 9, 2010, 02:22 AM
    More detail
    Duke911's Avatar
    Duke911 Posts: 11, Reputation: 1
    New Member
     
    #3

    Feb 9, 2010, 09:03 AM

    Brock CCC forced air furnace with through the wall ventilator. Beckett AFG Burner, 100PSI Oil Pressure, 0.75 80' nozzle. Currently 02 = 8.9, CO2 = 8.9, CO = 0, Net Stack Temp = 677F, Eff = 71, and Ex Air = 70
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Feb 9, 2010, 10:51 AM
    I see where you are headed. Your best bet is to go to the Beckett web site and look up that burner. It should contain info you are looking for.
    Duke911's Avatar
    Duke911 Posts: 11, Reputation: 1
    New Member
     
    #5

    Feb 10, 2010, 10:11 AM

    Thanks for the reply. The Beckett website says to back off the air until a trace of smoke is seen in the flame, then add air to drop CO2 reading by 2%. Does anybody who does flue gas analysis know what typical readings are?
    tk03's Avatar
    tk03 Posts: 33, Reputation: 2
    Junior Member
     
    #6

    Feb 10, 2010, 10:17 AM

    The typical CO2 is between 11 and 12.5. Draft on negative draft appliances should be -0.02 over fire. The stack will vary greatly per unit.
    Excess air is normally around 25%
    Duke911's Avatar
    Duke911 Posts: 11, Reputation: 1
    New Member
     
    #7

    Feb 10, 2010, 04:56 PM

    Thank you for the info. As I suspected, my current readings show way too much air. I will try trimming down the air shutter to bring my CO2 up above 11.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bio Claire results in steps! I am posting results you post yours! [ 34 Answers ]

Hello World! So I got my bio cliare creame, lotion, and oil appx.8 days ago. I have seen some lightening (more skin evening than anything) and now I am starting to itch a little but I see that's just apart of the process because it dries your skin a bit and I know I have to buy a sun screen to put...

Analyzing SF6 gas test results [ 1 Answers ]

Where can guidelines for analyzing SF6 gas test results for High Voltage Breakers?

I broke NC, but it worked out well (results not typical)! [ 5 Answers ]

Well here's a bit of a different story. I work for an online videogame company and I am given the game currency to purchase items in game as compensation for my volunteer work. I was going to go on a buy some items for a friend of mine, since I don't really play the games any more (I just...

Who did this song: from the 80's, probably called "typical" or "that's typical" [ 2 Answers ]

Some lyrics as I hear them: Windowsill, my elbow's numb As I heard the door go and saw your car As it glides onto the road Double wasted dumbness Sodding off and I can't hear you go And that's typical There you sit in the driving seat

Gas burner flue? [ 3 Answers ]

I just had my fireplace flue cleaned on my recently purchased 50-yr-old house. The service guy told me that the other flue -- the one to my gas burner -- was very damaged and needed to be relined. Is this possible? The house was converted from oil to gas about 20 years ago, and the gas burner...


View more questions Search