  • Feb 8, 2010, 10:48 PM
    Duke911
    What are typical flue gas results in a AFG
    What are typical flue gas results in a AFG
  • Feb 9, 2010, 02:22 AM
    hvac1000
    More detail
  • Feb 9, 2010, 09:03 AM
    Duke911

    Brock CCC forced air furnace with through the wall ventilator. Beckett AFG Burner, 100PSI Oil Pressure, 0.75 80' nozzle. Currently 02 = 8.9, CO2 = 8.9, CO = 0, Net Stack Temp = 677F, Eff = 71, and Ex Air = 70
  • Feb 9, 2010, 10:51 AM
    hvac1000
    I see where you are headed. Your best bet is to go to the Beckett web site and look up that burner. It should contain info you are looking for.
  • Feb 10, 2010, 10:11 AM
    Duke911

    Thanks for the reply. The Beckett website says to back off the air until a trace of smoke is seen in the flame, then add air to drop CO2 reading by 2%. Does anybody who does flue gas analysis know what typical readings are?
  • Feb 10, 2010, 10:17 AM
    tk03

    The typical CO2 is between 11 and 12.5. Draft on negative draft appliances should be -0.02 over fire. The stack will vary greatly per unit.
    Excess air is normally around 25%
  • Feb 10, 2010, 04:56 PM
    Duke911

    Thank you for the info. As I suspected, my current readings show way too much air. I will try trimming down the air shutter to bring my CO2 up above 11.