    Lennox furnace voltage to gas valve
    I have a Lennox G20Q3E-75-1 furnace. The ignitor lights the pilot light but not the burner. The ignitor never shuts off. The fan blower will come on after about a minute or so but the burner never lignts. Any ideas??
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #2

    Dec 29, 2009, 05:52 PM

    Most likely, the ignition module has failed. Once pilot flame is proven, the module powers the main gas control AND initiates the blower-on delay. If the blower operates, the gas control should too.
    njk53's Avatar
    njk53 Posts: 8, Reputation: 1
    New Member
     
    #3

    Dec 29, 2009, 05:55 PM

    Do you know what the voltage should be to the PV, MV, and PV/MV terminals should be when trying to start?
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #4

    Dec 29, 2009, 06:07 PM

    After blower starts, check for 24-27v between MV & PV/MV. If present, the gas control is bad. If not, the ignition module is bad.
    njk53's Avatar
    njk53 Posts: 8, Reputation: 1
    New Member
     
    #5

    Dec 29, 2009, 06:17 PM
    When starting up there was 25vAC at terminal PV. The was 0vAC athterminal MV and MV/PV. However, I don't think the fan was running when I checked the voltages.
    njk53's Avatar
    njk53 Posts: 8, Reputation: 1
    New Member
     
    #6

    Dec 29, 2009, 06:23 PM

    When I check the voltagewhen fan is in operation, do I check terminal MV to ground and terminal MV/PV to ground? Or do I use one of the terminals as ground?
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #7

    Dec 29, 2009, 06:24 PM
    Quote Originally Posted by njk53 View Post
    I don't think the fan was running when I checked the voltages.
    If the pilot lights, then NOTHING happens, try carefully removing & cleaning the flame sensor mounted to the pilot assembly. This is a much different scenario than what you previously described (pilot + blower, no main burner operation).
    Attached Images
      
    njk53's Avatar
    njk53 Posts: 8, Reputation: 1
    New Member
     
    #8

    Dec 29, 2009, 06:34 PM

    Sensor is brand new.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #9

    Dec 29, 2009, 06:36 PM

    P.S. Use PV/MV as ground.
    njk53's Avatar
    njk53 Posts: 8, Reputation: 1
    New Member
     
    #10

    Dec 29, 2009, 06:37 PM

    When checking the PV/MV terminal should I use MV as ground?
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #11

    Dec 29, 2009, 06:38 PM
    Quote Originally Posted by njk53 View Post
    Sensor is brand new.
    O.K. don't bother trying to clean it then. Turn up thermostat to demand heating, wait for blower to start (if it does), THEN check voltage between MV & PV/MV.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #12

    Dec 29, 2009, 06:40 PM
    Quote Originally Posted by KC13 View Post
    P.S. Use PV/MV as ground.
    Re-read thread.
    njk53's Avatar
    njk53 Posts: 8, Reputation: 1
    New Member
     
    #13

    Dec 29, 2009, 06:55 PM

    I will log on tomorrow and let you know the results. Thank You, you have been a big help.
    njk53's Avatar
    njk53 Posts: 8, Reputation: 1
    New Member
     
    #14

    Jan 7, 2010, 07:40 PM
    KC13 and Builder Bob, Thank you very much for the help. Your advise was spot on and helped me to diagnose the problem. The root cause of the problem was the ignitor box. I ordered one online for $118. Put it in today. The old Lennox is now purring like a kitten.

    Thanks Again
    NJK
    builderbob1's Avatar
    builderbob1 Posts: 41, Reputation: 2
    Junior Member
     
    #15

    Jan 8, 2010, 01:16 AM

    Just check for 24 volts at main gas valve if you have voltage and no gas the valve is bad. Check and make sure the gas valve is in the on position.If no voltage check all safetys and switchs before valve for voltage opr condanuity.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Lennox Pulse Gas Furnace? [ 5 Answers ]

I am having a diagnostic "nightmare"... only due to lack of knowledge of the Lennox Pulse. This is a roughly '90 model. 80,000 BTU... The problem: Furnace lights for about 10 sec- 2 minutes... shuts down... It resembles a primary air problem, sounds of the fire sucking air. A previous tech just...

Lennox G12 - Replacing Gas Valve [ 1 Answers ]

10/25/09 I have an old Lennox G12RQ3-82 furnace with a Robertshaw 7000 gas valve. Can I Switch out this standing pilot unit with an intermittent pilot model, say a White Rogers 36E gas valve? I want to upgrade the system so that I'm not burning a pilot light 24-7 all winter. Any...

Furnace dropping voltage at gas valve [ 1 Answers ]

I was checking voltage at the gas valve on a coleman furnace and my reading was 18 volts. What would cause the drop in voltage? I do have 24v into the board.

Crazy voltage at 2 stage gas valve [ 13 Answers ]

I have a 3 month old 2 stage goodman gas furnace that is making a clicking sound at the gas valve. What happens is when the themastat calls for heat the draft motor turns on and that's when the clicking sound begins at the gas valve. I took a voltage reading at the gas valve during this clicking...

Trane XL80 No Voltage to Gas Valve [ 2 Answers ]

TRANE XL80 Propane Furnace not working I have an older TRANE XL80 (1989) recently quit working. I discovered the ignitor was not glowing and traced it to a bad relay in the control module. I had the relay replaced, now the ignitor will come on and the unit fires up but will only burn for about 10...


View more questions Search