    How to wire electric on E3EB-015H
    The old furnace had 4 ac wires. 2 coming off a 60 amp from breaker box and 2 coming off 2 thirty amp tied together in breaker box. The new furnace a Miller (Nordyne) has 4 lugs. The top is empty, second one down has a 60 amp breaker, third is empty and fourth has a 60 amp breaker. It came with a single circuit adaptor. Does the two 60 amp wires go to the 60 amp breakers and the two 30 amp go to the empty slots? Should I use the single circuit adaptor? The old furnace was a Intertherm model FEH-015HA-03. Any one who owns the old furnace should check for corrosion. Melted and burned up buse fuse.

    Thanks, Doug
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #2

    Nov 14, 2009, 05:20 PM

    Sounds like you have a bigger kw heating element in this new unit if it has 2 60 amp breakers. You may need to unhook a element or run bigger wire.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #3

    Nov 14, 2009, 06:40 PM
    Should I use the single circuit adaptor?

    NO

    The unit you have has 2 breakers according to the install instructions below.

    http://www.nordyne.com/Literature/708322d.pdf

    Follow the instructions

    In that model of unit it should have 3 heaters in total. One is on a 20 amp circuit fed by a 30 amp breaker and the other two heater circuit goes on the 60 amp breaker.

    Now if your new heater has two 60 amp breakers then something is wrong with that picture because your model number you posted (E3EB-015H ) is supposed to have a 30 and a 60 amp breaker. READ the install instructions and page 22. It tells you what size wire goes to each breaker etc.
    ideliver's Avatar
    ideliver Posts: 3, Reputation: 1
    New Member
     
    #4

    Nov 14, 2009, 11:15 PM
    That is the correct manual. If you look on page 25 it shows 2 60 amp breakers dual supply. The ad I saw for it said it takes 2 sixty amp and one thirty amp. If the two sixties go to the breakers which lug does the thirty go to? The schematic shows line voltage but not how much. Page 21 shows supply circuit single, Dual A, Dual B is that 3 different ways to wire it up? Also it shows copper wire size, how do you find out the size of the wire? The front of the furnace has a picture across from the breakers. The top says circuit B and shows 2 small wires and the bottom says circuit A and shows 2 larger wires. Glad it is still warm here in Ohio. Thanks for your help.
    ideliver's Avatar
    ideliver Posts: 3, Reputation: 1
    New Member
     
    #5

    Nov 17, 2009, 03:38 PM
    I had my brother ask at work. The two 60 amp go on the bottom (circuit A) and the two 30 amp go on top (circuit B). Works fine.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Nov 17, 2009, 05:39 PM
    Glad you got it going

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Electric Fuse Wire [ 3 Answers ]

Kindly let me know, which compound is used in a fuse wire used in electric circuits

How do I wire a Miller furnace (E3EB-15H)? [ 1 Answers ]

Hello, I recently bought a new furnace and need help hooking up the thermostat and power. I have a very basic understanding of wiring, but don't want to mess this up. Any help will be greatly appreciated. Here's what I have: Furnace model number: E3EB-015H Power supply 240VAC 1Ph 60 Hz 4...

2 wire electric outlet to 3 wire [ 2 Answers ]

Can you just replace a 2 wire outlet with a 3 wire? My dau bought an old house that has 2 wire outlets and does not have the money to replace all the wire with 3 wires. We just want to replace the 2 wire outlet with 3 wire and only use 2 wires to do this.

Electric wire 10/3 [ 4 Answers ]

I have a 200 amp panel with a 10/3 wire running to a shed, then hooked to a 110 receptable. My question is can I take the 10/3 wire and change the 110 circuit to 220 ? Thanks Dave

Diconnect Intertherm FEH 015H [ 2 Answers ]

I cannot pull out the Disconnect on the lower right side of the inside heating unit of the Intertherm FEH 015H 017H. Does it come completely out? Could it be stuck? It doesn't seem to budge and I'm not that much of a weakling. Thank you for any information. Patt aka pattusa


View more questions Search