Trouble installing honeywell thermostat
I have a very old thermosat that has six wires hooked up to it now. It is labeled
2-white wire
0-brown wire
B-blue wire
R-red wire
Y-yellow wire
G-green wire
The honey well thermostat I bought has 5 connections Rh, Rc, W, Y, G with it only having 5 and my current has 6 is this thermostat going to work or not? I appreciate any info. Thank you so much
|
|
|
Ultra Member
|
|
Feb 22, 2009, 08:44 AM
|
|
The "O" circuit suggests that you have a heat pump, or some device that is powered when cooling is selected. If the brown wire is actually used/connected to something, the thermostat you have won't work.
|
|
|
Uber Member
|
|
Feb 22, 2009, 08:45 AM
|
|
The 6th may not be hooked up or needed.
Would be good to check in air handler what each wire is connected to and controls.
Often, Red is common power, white is heat,
Blue may be cool, and green for the fan.
The extra wire may be from the other side of the transformer.
|
|
|
New Member
|
|
Feb 22, 2009, 08:54 AM
|
|
Originally Posted by Stratmando
The 6th may not be hooked up or needed.
Would be good to check in air handler what each wire is connected to and controls.
Often, Red is common power, white is heat,
blue may be cool, and green for the fan.
The extra wire may be from the other side of the transformer.
What would be the best way to check if wires are working?
|
|
|
Ultra Member
|
|
Feb 22, 2009, 09:04 AM
|
|
Originally Posted by JustinJ15
what would be the best way to check if wires are working?
Trace them to find out what, if anything, they are connected to. P.S. The "Y" (yellow) is typically used for control of cooling and/or heat pump circuit.
|
|
|
Uber Member
|
|
Feb 22, 2009, 03:12 PM
|
|
Strat: Terminology problem
Originally Posted by Stratmando
Often, Red is common power
Red is usually 24 Vac.
Common is the lead they left out when the stats were mercury switch based. Common is necessary if the stat needs continuous power.
|
|
|
Uber Member
|
|
Feb 22, 2009, 04:21 PM
|
|
I was referring red as to being common with respect to each circuit, as a rotary switch has a common and out to numerous poles. Heat, compressor, contactor, blower.
Forgive my termonology.
I would look in Air Handler.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Installing a Honeywell Programmable Thermostat
[ 3 Answers ]
Hi:
Got a fixer-upper; need to install a Honeywell RTH6300 5-2 Day Programmable thermostat. I have the wires, the old unit was just yanked out of the wall. 6 wires... black/white/red/orange/green/"cream"?
Problem is they are not marked. How do I determine which wire goes to which terminal...
Installing new honeywell thermostat old wiring odd
[ 3 Answers ]
Hi
I bought a new thermostat a Honeywell rth7400 for heatpump & aux (oil as back up)
The old thermostat was a totaline with a separate toggle installed underneath it to switch back and forth from auxiliary to heat pump I have 8 wires coming out of the wall I have tagged them as followed:...
Installing a Honeywell programmable thermostat
[ 1 Answers ]
I am replacing an old mercury thermostat with a honeywell rth7000. I have a heat pump
Unit.
Current Mercury wired as such:
Red wire to R
Brown wire to T
Orange wire to O
Green wire to G
Yellow wire to Y
Blue wire to B
Installing RTH7400 Honeywell Thermostat
[ 1 Answers ]
I am replacing my (old) Honeywell T8411R thermostat with a (new)Honeywell RTH7400 programmable thermostat. I need help wiring to the new thermostat. My H/C system is a heat pump system.
The old thermostat is wired to the following terminals:
W1 - White
W2 - Brown
G - Green
R - Red
C - Blue...
View more questions
Search
|