    Trouble shouting
    Hi,
    I have a outdoor split system heat pump YORK E4FD AND A THERMOSTAT VICONICS
    CBE-118 . It indicated code 06. I cannot find this fault indication.
    The heat pumps restart after here defross cycle but stop and goes on emergency wich activated the funace for heating the house.
    Regards Paul:confused:
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Feb 12, 2009, 02:27 PM
    York guard system

    2 = discharge pressure over 400 psig
    3 = discharge line temp over 275 F
    4 = discharge line temp did not hit 90 F with 1 hour of call for compressor
    5 = 2 defrosts in 1 hour
    7 = OD Sensor open or shorted
    8 = Liquid line sensor open or shorted
    9 = Bonnet sensor shorted

    No 6 listed. Sure it is not a 9.
    pitrep's Avatar
    pitrep Posts: 3, Reputation: 1
    New Member
     
    #3

    Feb 12, 2009, 03:06 PM
    Quote Originally Posted by hvac1000 View Post
    York guard system

    2 = discharge pressure over 400 psig
    3 = discharge line temp over 275 F
    4 = discharge line temp did not hit 90 F with 1 hour of call for compressor
    5 = 2 defrosts in 1 hour
    7 = OD Sensor open or shorted
    8 = Liquid line sensor open or shorted
    9 = Bonnet sensor shorted

    No 6 listed. Sure it is not a 9.
    Yes it is a 06. That why I find it funny. Flashing 06
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Feb 12, 2009, 05:50 PM
    Dang it I have no idea on the 6 code but my manuals are not here at this time. Good luck finding the 6 code.
    pitrep's Avatar
    pitrep Posts: 3, Reputation: 1
    New Member
     
    #5

    Feb 17, 2009, 12:59 PM
    Quote Originally Posted by hvac1000 View Post
    Dang it I have no idea on the 6 code but my manuals are not here at this time. Good luck finding the 6 code.
    I found the probleme: The code 06 is probleme with plenum sensor. I change it and it now work perfectly. PS: indoor unit.
    Thank you.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Feb 17, 2009, 01:40 PM
    Good deal. I will put that in my log.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Shouting/Crying/Yelling in sleep [ 14 Answers ]

Just a question... Ever since I can remember, any one who has ever shared a room or house with me has often told me that I shout out, cry, argue, swear etc in my sleep. This can sometimes be phsycial too as I sometimes wake myself up if I kick the wall etc... I've always thought that this only...

Guy trouble [ 5 Answers ]

I'm a freshman and I have advanced classes in school so some of my classes are with older people, there is this junior in my science class and he is really cute. I just don't know how to get his attention I've caught his eye in the halls now and then but I've seen him kissing another girl, I don't...

Shouting in sleep [ 1 Answers ]

I have been regularly shouting in my sleep and also fighting and I have also been taken off olanzapine for schizophrenia and also depression tablets(citalopram) I have also been having disturbing dreams one of which is when I am coming home on a bus and someone from school is there and they show...


View more questions Search