    Tempstar Furnace Malfunction Blows cold No Heat Call
    Tempstar about 10 yrs old?? (was here when I moved in)
    (Model number: NUGS050AF01
    Gas/Has pvc pipes extending to outside at side of house.

    Is a split system

    No heat call. If I turn thermostat to on and turn up thermostat, nothing will happen.
    If I turn the heat from auto to run, the blower will go and cold air comes through.
    I do hear the gas click, I hear some other clicking.
    I cannot see any ignition action
    Draft inducer is on right away.

    I have had limit switch problem before. Tons of times and no matter who I paid to help me, it did not ever get fixed properly. I had another contractor come out, and we worked on it all day. Put in a honeywell limit switch and new Ingition Control with LED indicators will do the normal yellow for two seconds, the green then (with no heat) will eventually blink Red. Slow single blinks.

    There, have I forgotten something? This happen very early this morning. I live in Minnesooooota and it got very cold last night.

    Oh, yes, I check for clogs in the pipes as well.

    I need real troubleshooters. I am a contractor by trade, but a General.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jan 8, 2009, 01:25 PM


    Is this what your blower unit looks like with the controls?

    Is so this is a Inner City unit unless says Tempstar.

    The model number you posted is incorrec. You might want to check the 4th letter/number since I believe that is the problem with my research on my digital manuals.
    cyberheater's Avatar
    cyberheater Posts: 321, Reputation: 12
    Full Member
     
    #3

    Jan 8, 2009, 01:45 PM

    I will check the number again, but it does say it's a tempstar and I got that number from inside of the furnace housing.

    The blower is below and only has the blower, no controls (but of course the wires from the controls)

    I took off the limit switch, it was quite long about 10 inches. Bigger then what I had in there before. At least one lasted for longer then a year. It's a honeywell. The camstat's are no longer available.

    Does this help
    cyberheater's Avatar
    cyberheater Posts: 321, Reputation: 12
    Full Member
     
    #4

    Jan 8, 2009, 01:49 PM
    Oh here is the serial number:
    L913825416
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Jan 8, 2009, 06:23 PM
    Have you tried to temp jumper the limit switch?

    Can you post the number (s) on the circuit board/control module since I cannot find your model number listed. I need this info to try and figure out what the blink code is saying unless you have a paper on the back of the blower door that has it listed.

    If you do not see a glow down at the burner then the ignitor or the circuit board could be bad but temp jump the limit out and see what happens.

    I also believe from what you posted in your first post that you could have a install problem since the limit control has caused many problems before. It could be cycling on the limit from time to time causing it to wear out. The limit control is never supposed to work unless your furnace has a heat removal problem.
    cyberheater's Avatar
    cyberheater Posts: 321, Reputation: 12
    Full Member
     
    #6

    Jan 9, 2009, 04:29 AM

    Wow. Good. I will try to that. Can you assist in reminding how to do that. I remember having to do this when this problem first occurred, but?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #7

    Jan 9, 2009, 05:08 AM
    I need this info first

    Can you post the number (s) on the circuit board/control module since I cannot find your model number listed. I need this info to try and figure out what the blink code is saying unless you have a paper on the back of the blower door that has it listed.
    cyberheater's Avatar
    cyberheater Posts: 321, Reputation: 12
    Full Member
     
    #8

    Jan 9, 2009, 07:10 AM

    Sorry, very tired and was not thinking clearly yet when I posted this A.M>

    I am looking for my jumper now, but to answer your question.

    The ignition control is a White Rodgers model
    50E47 I installed this in late fall of 2006 with another contractor. The LED Red "blink once"
    troubleshooter lists this:

    Reset control to clear lockout and confirm fault
    1 flash = Number of Retries exceeded, control locked out.

    I also went down the list. 1st. Yellow for two seconds, then green, then red slow blink (indicating actually on blink instead of fast two)
    And it tells me to check the volts to ignitor terminals. So that is the plan and I am now going to find that jumper or run quick to get one.

    After doing some checking, I found that the Model number is kind of a generic name, Used also in ICP. I also found that there are part numbers for limit switches that coinside with that model number I gave you, but of course it can't be found anywhere else. I wish my camera worked.

    The blower fan is located below on bottom of unit. The rest: Inducer, ignition and combustion chanber, pressure switch, limit switch, control panel, etc. on the top half.

    Horizontal piping. I checked for cracks in the PVC piping. NONE.
    cyberheater's Avatar
    cyberheater Posts: 321, Reputation: 12
    Full Member
     
    #9

    Jan 9, 2009, 07:15 AM
    OH in addition, after this happening so often and getting quite annoyed. =0 I had purchased a back up limit switch. Not a honeywell, but the older style from Dey Appliance and I have located it.

    Although, I found it in the box, I am a little stumped. No reading material specs to indicate how to hook up line and load and nothing on the limit switch either. Each brand is different, so I wanted to be sure.

    It is OEM HQ1005762CS
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #10

    Jan 9, 2009, 09:07 AM
    See if your control looks like one of these below. If yyes and you still cannot hook it up correctly email [email protected] at A-1 Cam stat.
    Attached Images
  1. File Type: pdf 8173000400.pdf (64.7 KB, 1958 views)
  2. File Type: pdf 8173007200.pdf (70.3 KB, 601 views)
  3. cyberheater's Avatar
    cyberheater Posts: 321, Reputation: 12
    Full Member
     
    #11

    Jan 9, 2009, 11:06 AM

    I am still trying to figure if I have to replace the limit switch. It's currently a honeywell, but I guessing I do.

    No, the pic you showed is not the back up I have. That one you show, I had replaced with the honeywell one two years ago.
    cyberheater's Avatar
    cyberheater Posts: 321, Reputation: 12
    Full Member
     
    #12

    Jan 9, 2009, 11:11 AM
    B1370910 Limit Switch L170

    Here is a closer pic of what I have, but the part number is wrong. It has to connections and neither of them are marked. It's important, I would think - No?

    Anyway - it's a part via ICP.
    cyberheater's Avatar
    cyberheater Posts: 321, Reputation: 12
    Full Member
     
    #13

    Jan 9, 2009, 11:32 AM

    I have a "fan control" already on this furnace in a different location. (contacts for gas valve, switch, etc) I only need limit switch.
    cyberheater's Avatar
    cyberheater Posts: 321, Reputation: 12
    Full Member
     
    #14

    Jan 9, 2009, 02:59 PM

    Okay, I have the new limit switch installed, but I still can't get the ignition surface to light up. I know my ignition control locks out, so I am checking that.

    Can I get some help with jump testing instructions?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #15

    Jan 9, 2009, 03:10 PM
    This is why there is a problem with helping further. Almost every number you have posted do not work.


    MODEL NUMBER SEARCH/CROSS REFERENCE
    Active Models/Obsolete Models/Competitive

    Your search for 50E47 did not return a result. Please re-enter your Model Number.



    To quickly locate information on a product or obtain a replacement suggestion enter the first few digits of a White-Rodgers or Competitive, Active or Obsolete Model Number and click “Submit”.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #16

    Jan 9, 2009, 03:11 PM
    Try the number again. It will have more numbers
    cyberheater's Avatar
    cyberheater Posts: 321, Reputation: 12
    Full Member
     
    #17

    Jan 9, 2009, 03:49 PM

    White Rodgers 50E47-843

    Sorry, I am trying to do this while helping a client of my own , etc. I get started, then the phone rings and everyone else is "LIKE URGENT" and the dogs want my attention, the kid wants me to take her for a driving lesson (and that makes me nervous)

    So, as far as you trying to help me? I am so sorry for making it harder on you to do it. I should be more relaxed, so no more coffee and I am not anwering any more "emergencies". I have enough of my own.

    You have been very patient and I appreciate that.
    cyberheater's Avatar
    cyberheater Posts: 321, Reputation: 12
    Full Member
     
    #18

    Jan 9, 2009, 03:53 PM
    I did just started her up.

    The inducer went on. (the control ignition went to LED yellow again, then to green solid, and the clicking was happening, but no hot surface ignition after I waited. I turned off the switch.
    Something else is going on. I need to troubleshoot this.

    There is no rust anywhere.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #19

    Jan 9, 2009, 03:58 PM
    Here is some info for you.Read it all. Everything you always wanted or needed to know is here.

    http://www.white-rodgers.com/wrdhom/...date121103.pdf


    http://www.white-rodgers.com/wrdhom/...pg0274_277.pdf

    http://www.white-rodgers.com/wrdhom/.../0037-6426.pdf


    http://www.white-rodgers.com/wrdhom/...ts/WR_8449.pdf
    cyberheater's Avatar
    cyberheater Posts: 321, Reputation: 12
    Full Member
     
    #20

    Jan 9, 2009, 04:54 PM

    Yep, that was good. It has already been installed previously, and I understand what it is telling me. I still can't get the hot surface ignition to start up after it tries to get it too.

    Not sure what to check next.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

I have a Tempstar Heater.The fan blows.no heat. [ 2 Answers ]

Here are the model / serial numbers... Model #... NDGE075RF01 867.768362 SERIAL #.. L912350186 My gas is on and we tried turning the thing off. My brother in law said that before there should be a clicking sound before the gas ignites... NO clicking sound... just blowing out air......

Why cold air blows out of cold air return when furnace is on [ 1 Answers ]

Why does cold air blow out of the cold air return when the furance is on?

Heat blows cold air [ 1 Answers ]

My daughter recently rented a house. The heat in the house blows cold air in two of the bedrooms and one vent in the dining room. The landlord is telling her these are return air ducts. If this is the case half of her house has no heat. Is this possible, there are what appear to be two return air...

CARRIER 58RAV Furnace Blows Cold Air-No Heat [ 1 Answers ]

I have a Carrier Model # 58RAV50-13112 Gas Furnace (fueled by propane) that isn’t working properly. It’s a holiday weekend and I’m without heat, so any help would be greatly appreciated. The furnace was operating properly throughout last winter. However, now it‘s not working. The fan runs but...


View more questions Search