Start up sequence on furnace is sporadic.
There are times when my Gas furnace Nordyne/Miller G3RA will do everything correct until it's time to introduce gas for ignition. The chamber motor starts, the glow plug lights I even hear the gas valve click open. The problem is sometimes it will immediately click closed.This may happen several times in succession until it eventually stays open (GAS VALVE) or the furnace stops trying and all you have is cold house and a running chamber motor.To make things even more interesting I've observed the glow plug light after the furnace had ignited.(This doesn't usually happen)
|
|
 |
Heating & Air Conditioning Expert
|
|
Dec 31, 2008, 05:34 PM
|
|
|
|
 |
Heating & Air Conditioning Expert
|
|
Dec 31, 2008, 05:47 PM
|
|
Try cleaning the flame sensor.
|
|
 |
New Member
|
|
Dec 31, 2008, 06:35 PM
|
|
First try still a little shaky... hesitated once or twice but did start. Replace it? Does this item fail often.
|
|
 |
Heating & Air Conditioning Expert
|
|
Dec 31, 2008, 06:43 PM
|
|
The flame sensor usually does not fail BUt it does get dirty. If it makes you feel better replace it.
|
|
 |
New Member
|
|
Jan 1, 2009, 09:35 PM
|
|
Cleaned flame sensor w/emery cloth. Problem still exists. If I turn furnace off and back on it may operate correctly.There have also been times when I've done that procedure over and over 5 or more times brfore it ignites. I also noticed glow plug turn back on after furnace ignited. Any suggestions would be greatly appreciated.
|
|
 |
Ultra Member
|
|
Jan 1, 2009, 09:44 PM
|
|
A faulty pressure switch can produce this situation (doesn't support current when gas control is powered).Try this: remove C and NO wires from pressure switch, start unit, and jump wires together. See if unit runs normally, but only do this to test for faulty pressure switch. The ignitor is in the fire stream, and after several seconds the heat built up in the element can result in a glow, giving the appearance that it has been powered again.
|
|
 |
Senior Member
|
|
Jan 1, 2009, 10:02 PM
|
|
The flame sensor will not be a factor unless you actually get ignition. Do you have an electrical meter? Can you test across the pressure switch and/or the coil on the gas valve?
|
|
 |
New Member
|
|
Jan 2, 2009, 12:41 AM
|
|
Thank you for the advice... I am not getting any ignition when it fails. Everything works fine until it's time to introduce the gas. I tested the pressure switch as suggested and it is working correctly. I do have a meter... How do I test the gas valve?
|
|
 |
Heating & Air Conditioning Expert
|
|
Jan 2, 2009, 03:00 AM
|
|
Put the meter on the AC scale and hook up the meter to the gas valve power wires that you have removed from the gas valve. Turn on furnace and wait to see if any voltage registers on the meter. You will need to watch the meter carefully since the gas valve voltage will drop out on the safety.
If you have the UTEC control board you might also try and remove and replace the 6 pin plug up near the HUM and EAC terminals since that has been proven to be a weak spot for electrical transfer on this circuit board and this plug also carry's power to the gas valve. This could explain the intermittent nature of your problem.
See attachment below.
|
|
 |
New Member
|
|
Jan 2, 2009, 12:29 PM
|
|
House is warm again!! All of your assistance helped me eliminate everything with the exeption of the gas valve and the ignition control modual. Replaced ignition modual and furnace is working as intended. Family and I are very thankful.
|
|
 |
Heating & Air Conditioning Expert
|
|
Jan 2, 2009, 02:42 PM
|
|
Glad you finally got the furnace working.
|
|
 |
Senior Member
|
|
Jan 2, 2009, 05:57 PM
|
|
Good to hear, congrats.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Furnace ignites but blower won't start till furnace shuts down.
[ 7 Answers ]
(Nordyne/Miller G3RA)-I have a furnace HSI(glow plug) that will ignite and burn until it gets too hot and shuts down. As soon as the furnace shuts down the blower starts to circulate air. The blower circulating air cools the furnace and it reignites.Shortly after the furnace ignites the blower...
Furnace turn on sequence
[ 2 Answers ]
My Bryant Furnace works OK, except that it doesn't seem to be firing up in the proper sequence. Pilot light should ignite and then a short time later burners should ignite and blower should start. As unit is now, blower starts same time as pilot light goes on and then after a few seconds the...
Furnace runs sporadic - on and off all night
[ 10 Answers ]
I have an older furnace (20+ years) and it is keeping us up at night. We had some extra ducts put in when we finished the basement and at the time we were right at the edge of what the furnace could run (it is approx 55% effecient).
The house is always cool and not a lot of heat reaches the...
'95 Honda Civic sporadic overheating
[ 1 Answers ]
My '95 Honda Civic DX has been overheating, but only at certain times. It seems to happen after I've been driving on the highway for a while (often with big hills) and suddenly slow down (i.e. hit traffic or get off onto local roads). I had the thermostat replaced a couple months ago, which...
View more questions
Search
|