    blkjagg
    Start up sequence on furnace is sporadic.
    There are times when my Gas furnace Nordyne/Miller G3RA will do everything correct until it's time to introduce gas for ignition. The chamber motor starts, the glow plug lights I even hear the gas valve click open. The problem is sometimes it will immediately click closed.This may happen several times in succession until it eventually stays open (GAS VALVE) or the furnace stops trying and all you have is cold house and a running chamber motor.To make things even more interesting I've observed the glow plug light after the furnace had ignited.(This doesn't usually happen)
  • Dec 31, 2008, 05:34 PM
    hvac1000
    What? Read this post


    https://www.askmehelpdesk.com/heatin...ml#post1455477
  • Dec 31, 2008, 05:47 PM
    hvac1000
    1 Attachment(s)
    Try cleaning the flame sensor.
  • Dec 31, 2008, 06:35 PM
    blkjagg

    First try still a little shaky... hesitated once or twice but did start. Replace it? Does this item fail often.
  • Dec 31, 2008, 06:43 PM
    hvac1000
    The flame sensor usually does not fail BUt it does get dirty. If it makes you feel better replace it.
  • Jan 1, 2009, 09:35 PM
    blkjagg

    Cleaned flame sensor w/emery cloth. Problem still exists. If I turn furnace off and back on it may operate correctly.There have also been times when I've done that procedure over and over 5 or more times brfore it ignites. I also noticed glow plug turn back on after furnace ignited. Any suggestions would be greatly appreciated.
  • Jan 1, 2009, 09:44 PM
    KC13
    A faulty pressure switch can produce this situation (doesn't support current when gas control is powered).Try this: remove C and NO wires from pressure switch, start unit, and jump wires together. See if unit runs normally, but only do this to test for faulty pressure switch. The ignitor is in the fire stream, and after several seconds the heat built up in the element can result in a glow, giving the appearance that it has been powered again.
  • Jan 1, 2009, 10:02 PM
    MarkwithaK

    The flame sensor will not be a factor unless you actually get ignition. Do you have an electrical meter? Can you test across the pressure switch and/or the coil on the gas valve?
  • Jan 2, 2009, 12:41 AM
    blkjagg

    Thank you for the advice... I am not getting any ignition when it fails. Everything works fine until it's time to introduce the gas. I tested the pressure switch as suggested and it is working correctly. I do have a meter... How do I test the gas valve?
  • Jan 2, 2009, 03:00 AM
    hvac1000
    1 Attachment(s)
    Put the meter on the AC scale and hook up the meter to the gas valve power wires that you have removed from the gas valve. Turn on furnace and wait to see if any voltage registers on the meter. You will need to watch the meter carefully since the gas valve voltage will drop out on the safety.

    If you have the UTEC control board you might also try and remove and replace the 6 pin plug up near the HUM and EAC terminals since that has been proven to be a weak spot for electrical transfer on this circuit board and this plug also carry's power to the gas valve. This could explain the intermittent nature of your problem.
    See attachment below.
  • Jan 2, 2009, 12:29 PM
    blkjagg

    House is warm again!! All of your assistance helped me eliminate everything with the exeption of the gas valve and the ignition control modual. Replaced ignition modual and furnace is working as intended. Family and I are very thankful.
  • Jan 2, 2009, 02:42 PM
    hvac1000
    Glad you finally got the furnace working.
  • Jan 2, 2009, 05:57 PM
    MarkwithaK

    Good to hear, congrats.