    Fan Heaters Installation
    Happy New Year everyone!

    I want to install 2 x 5000W fan heaters in my garage.

    I need to install a sub panel about 15ft from the electrical room.

    The subpanel will only have 2 x30A breakers in it for the heaters but my question is what size breaker do I need in the main panel? Also would 6/3 wire be sufficient between the main panel and subpanel(a 70A Stablok panel)?

    Thanks
    John
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Jan 1, 2009, 09:49 AM
    Yes, 6/3NM cable would be fine to use to feed the sub-panel. You would be limited to a 60A feeder breaker though. IMO that would be fine in your case, and even leave a little room for expansion.
    terreneuve's Avatar
    terreneuve Posts: 15, Reputation: 1
    New Member
     
    #3

    Jan 1, 2009, 11:33 AM
    Quote Originally Posted by stanfortyman View Post
    Yes, 6/3NM cable would be fine to use to feed the sub-panel. You would be limited to a 60A feeder breaker though. IMO that would be fine in your case, and even leave a little room for expansion.
    Thanks! One last question though - I have 10/3 NM for wiring the heaters and wonder why is it coloured orange - is it a standard colour for heater cable?? I have seen in different size cables you can get blue, black etc..

    Might be a stupid question but like everything there has to be a reason!
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Jan 1, 2009, 12:17 PM
    In the US smaller NM cable has been coming in colors. This is not a code thing, it is just a manufacturer thing. #14 is still white, but #12 is yellow and #10 is orange.

    You in fact do not need 10/3. You can use 10/2 for your straight 240v heater circuits. Although, you spell is colour. Are you in Canada? If so I believe you guys have a special red cable with just a black and red conductors for 240v circuits. I don't know the actual code on this though.
    terreneuve's Avatar
    terreneuve Posts: 15, Reputation: 1
    New Member
     
    #5

    Jan 1, 2009, 03:06 PM
    Quote Originally Posted by stanfortyman View Post
    In the US smaller NM cable has been coming in colors. This is not a code thing, it is just a manufacturer thing. #14 is still white, but #12 is yellow and #10 is orange.

    You in fact do not need 10/3. You can use 10/2 for your straight 240v heater circuits. Although, you spell is colour. Are you in Canada? If so I believe you guys have a special red cable with just a black and red conductors for 240v circuits. I don't know the actual code on this though.
    Canada is right! 10/2 is right -I made a typo. That's correct about the red covered 12/2.

    It's funny some words here are spelled differently and vary between provinces(not just Quebec) and also pronounced completely different too!

    Our code here is very close to US as are the plumbing and building codes.

    I think in Canada for some applications cable color:) is mandatory but some one could probably correct me on that!

    Thanks again!
    John

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Baseboard heaters [ 11 Answers ]

I am getting ready to put in 4 baseboard heaters 3 of them will be in one room upstairs and the other downstairs. I need help wiring them all. Let me clarify, the 3 baseboard heaters need to be wired together on one breaker and the other will be on its own breaker. Help.

2 Heaters on 1 220 line? [ 1 Answers ]

I have a 2000 Watt 220 convection heater and would like to add another one to the same wire. Can this be done? Is it the circuit breaker tripping or melting of the wire that is the danger? Thanks

Electric baseboard heaters -wiring 1 thermostat to two heaters [ 2 Answers ]

I would like to heat my new garage with electric baseboard heaters. The new garage is 20X24 feet. I would like to use only one 240V #12 2 wire circuit running two heaters at a total of 3800 watts. I plan to use 2 pole 20A breakers and 2c #12 wire. I would like to have both heaters controlled...

Baseboard heaters [ 1 Answers ]

Hello, Are there any rules for running #10 to Junction boxes in basement right below heaters and tapping off with 12/2 to them less than 6'. I'm running 30 amp circuit for 6000 watts of baseboard heat in parallel


View more questions Search