My Goodman furnace shows a one blink code that translates to ignition failure and suggests checking the flame sensor (which I replaced) the gas valve (which I replaced) gas pressure (had new gas meter installed) or restricted gas flow (which I can't imagine) Any help is greatly appreciated.
|
|
 |
Ultra Member
|
|
Dec 20, 2008, 11:00 PM
|
|
Is the igniter working(glowing) when it should be?
The steps for a furnace to start up and work proper
1. the thermostat calls for heat
2. the inducer motor starts up (maybe for 30 sec.
3. the igniter comes on (glows)
4. the gas valve then opens and burners fire up
5. after maybe 1 minute the blower comes on and blows heat into ductwork which routes heat into house
The gas valve won`t open up until the igniter comes on
|
|
 |
Ultra Member
|
|
Dec 20, 2008, 11:00 PM
|
|
Observe operating sequence, should go like this: 1) inducer starts/runs, 20-40 seconds 2) ignitor glows, 17-34 seconds 3) gas control opens & burners light, 25-40 seconds 4) blower starts/runs for duration of heating cycle. Post back.
|
|
 |
Ultra Member
|
|
Dec 20, 2008, 11:01 PM
|
|
 Originally Posted by wmproop
is the igniter working(glowing) when it should be?
the steps for a furnace to start up and work proper
1. the thermostat calls for heat
2. the inducer motor starts up (maybe for 30 sec.
3. the igniter comes on (glows)
4. the gas valve then opens and burners fire up
5. after maybe 1 minute the blower comes on and blows heat into ductwork which routes heat into house
Damn! It's true, great minds do think alike...
|
|
 |
Ultra Member
|
|
Dec 20, 2008, 11:06 PM
|
|
 Originally Posted by razorface
My Goodman furnace shows a one blink code that translates to ignition failure and suggests checking the flame sensor (which I replaced) the gas valve (which I replaced) gas pressure (had new gas meter installed) or restricted gas flow (which I can't imagine) Any help is greatly appreciated.
You may have replace the flame sensor and gas valve and didn`t need to,, the flame sensor very seldom goes bad,, (just needs cleaning with fine sandpaper)
The gas valve won`t open till the flame sensor sees the igniter glowing
|
|
 |
New Member
|
|
Dec 21, 2008, 08:37 AM
|
|
The gas valve is not opening and so the burners do not light.
|
|
 |
New Member
|
|
Dec 21, 2008, 08:38 AM
|
|
The igniter is glowing hot
|
|
 |
New Member
|
|
Dec 21, 2008, 08:47 AM
|
|
The igniter isworking but the gas valve is not
|
|
 |
Ultra Member
|
|
Dec 21, 2008, 09:36 AM
|
|
Check the string of limit switches that surround the burner assembly. Follow the purple wires from one to the next, press the tab in the center, see if any of them are popped. If so you may have a heat exchanger leak.
|
|
 |
New Member
|
|
Dec 21, 2008, 09:48 AM
|
|
Is there a way to bypass the limits directly to see if the limit connections are bad?
|
|
 |
Ultra Member
|
|
Dec 21, 2008, 09:51 AM
|
|
Follow my earlier suggestion and check for any that are popped. This is the next step, trust me. These are there for a reason and should not be bypassed.
|
|
 |
New Member
|
|
Dec 21, 2008, 09:55 AM
|
|
Also ,how can you find a leak in the heat exchanger?
|
|
 |
Ultra Member
|
|
Dec 21, 2008, 09:57 AM
|
|
Observe. If the flames start blowing stray when the blower starts, you have a problem. If the burner limit(s) are tripped, it's a bad sign that this is happening.
|
|
 |
New Member
|
|
Dec 21, 2008, 09:58 AM
|
|
None of the switches are popped and I have 28 volts at the gas switch
|
|
 |
New Member
|
|
Dec 21, 2008, 09:59 AM
|
|
The burners never come on
|
|
 |
Ultra Member
|
|
Dec 21, 2008, 10:07 AM
|
|
Do you hear the gas valve clicking during the ignition trial? If not, turn power off, pull wires off gas valve, and check continuity of gas valve coil.
|
|
 |
New Member
|
|
Dec 21, 2008, 10:09 AM
|
|
The gas valve does not click .There is a click at the circuit board after the igniter glows but the burners do not light and the blower does not come on
|
|
 |
Ultra Member
|
|
Dec 21, 2008, 10:13 AM
|
|
If you have a voltmeter, set it to ohms function and check gas valve coil. Infinite resistance would indicate a failed coil. Check for terminal oxidation while you're at it.
|
|
 |
New Member
|
|
Dec 21, 2008, 10:15 AM
|
|
I will do that now. Thanks for paying attention!
|
|
 |
New Member
|
|
Dec 21, 2008, 10:37 AM
|
|
The gas valve coil tower , if Iunderstand this is what you mean, is located in the gas valve itself. It is new and so are the connections. The ohm meter checked at these two terminals do not go to infinity but do show a little resistance
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Ignition failure carrier furnace
[ 1 Answers ]
Thk for the reply, I tried connecting a wire from the spark generator post and holding the other end 1/8 inch from the ground. First try a got a short burst of 3 weak sparks. Shut off furnace and re started this time no sparks a all. Checked that there was still voltage going to the SG unit. Guess...
Ignition proving failure
[ 12 Answers ]
Carrier model 58RAV. Once a month the heating system's led code shows 14 ignition proving failure,after a couple of hours it resets itself and everything is fine.What gives?
Ignition interlock failure
[ 5 Answers ]
What happens if someone who is court ordered to put a breathalyser in his or her fails a test? Is this a violation of probation? What is the probation officer's next move? Does the test record show the level of BAC or is a pass or fail kind of thing? This is all very to me, because technically...
Coleman, Evcon Ignition Failure
[ 1 Answers ]
A couple of years ago, there was a recall on a part that a Company had to come out and replace. I had never had a problem with the furnace for 8 years. A short time later, I started having problems with ignition failure. I had a part replaced and a licensed Company went over everything and said...
View more questions
Search
|