    Hi how many four tube fluorescent fittiings can you have on one 10 amp circuit in a commercial installation I know ten is the norm but have to be sure
    dinkinpoop's Avatar
    dinkinpoop Posts: 6, Reputation: 1
    New Member
     
    #2

    Dec 8, 2008, 07:21 AM

    You need the voltage supplied to the lights and the watts of each tube. Add your watts together then divide that by the voltage that will give you your amps. Lighting in the NEC is consider a contious load so your over current device can only be rated at 80%.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Dec 10, 2008, 03:39 AM
    Calculating the load of a fluorescent fixture is a bit more than just adding the wattage of the lamps.

    There is still the ballast factor.

    Each ballast has a nameplate that states the total amp draw, combining the wattage of the lamps and VA of the ballast.
    dinkinpoop's Avatar
    dinkinpoop Posts: 6, Reputation: 1
    New Member
     
    #4

    Dec 10, 2008, 04:09 AM
    Quote Originally Posted by tkrussell View Post
    Calculating the load of a fluorescent fixture is a bit more than just adding the wattage of the lamps.

    There is still the ballast factor.

    Each ballast has a nameplate that states the total amp draw, combining the wattage of the lamps and VA of the ballast.
    Good to know. I learned something new

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Theory of vacuum Circuit Breaker & sf6 circuit breaker [ 15 Answers ]

I want to know about the basic Theory of vacuum Circuit Breaker & sf6 circuit breaker

Changing 15 amp circuit to 20 amp circuit [ 4 Answers ]

I just bought a house with a jaquzzi that was installed by the previous owner. It appears that they wired it to an existing circuit run that is only pulling 15amps. So if the lights are on in the bath room and in the closet, when we turn on the jaquzzi it trips the breaker. Before I open up the...

Converting 15 anp circuit into 20 amp circuit [ 1 Answers ]

I just bought a treadmill. The problem is it doesn't work where I want it to. It can only run on 20 amps but all my outlets use 15 amps. It keeps tripping the breaker. Can I easily convert my outlet to a 20 amp?

Motion Sensor switch with compact flourescents [ 2 Answers ]

I recently installed a 3-position motion sensor switch (off/auto/on) to replace a simple 2-way decora rocker for the recessed pots in my laundry. There are 3 of them. Immediately after installing them, I noticed the lights flickering when in auto mode and also a low hum eminating from the breaker...

Outside GFI circuit - 15amp outlet on 20amp circuit [ 1 Answers ]

I need a better understanding of what I should do when setting up my new outdoor circuit. I've got a circuit that runs about 150 feet, so I'm installing 10g wire to allow for the voltage drop. I read in the Home Depot Electrical 123 book that I can have at most a 15amp circuit with 10g wire on...


View more questions Search