    220 breaker connection
    I'm adding a 220 volt circuit. It appears to me that the breaker (20 amp, 2 pole in a GE panel) is only going to pull power from one of the two bars in the box. For 240, wouldn't the breaker need to tap into the bars on each side? Am I over-thinking this?

    Thanks.
    smearcase's Avatar
    smearcase Posts: 2,392, Reputation: 316
    Ultra Member
     
    #2

    Aug 13, 2008, 07:25 PM
    I believe you are overthinking. If it is the right breaker for the panel, it will produce 220 volts. If you were to put two single pole breakers side by side, they will tap into two different phases and produce 220 if you were to measure with a meter.
    LKarnes's Avatar
    LKarnes Posts: 3, Reputation: 1
    New Member
     
    #3

    Aug 13, 2008, 07:52 PM
    Thanks.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #4

    Aug 13, 2008, 09:43 PM
    Your are correct that the breaker must tap into both sides of the panel to give you 240 volts. A double breaker does that. The panel is what's called a split buss panel. Any two spaces down one side of the panel come from opposite legs of the service.
    Attached Images
     

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can a breaker cause a "bad connection" but not trip? [ 1 Answers ]

I bought a new hot water heater last month and when the guy installed it and switched on the power, he said it didn't immediately work (second try it worked).. that maybe there was a breaker problem... now it's been a month and every now and then there isn't enough hot water... it has never run out...

Replacing GFCI Breaker With A Regular Breaker [ 1 Answers ]

I have a 15 amp circuit serving only a single outlet on my deck. It is protected by a GFCI circuit breaker in the home's single 125 amp service panel. I wish to replace the GFCI breaker with a regular 15 amp GE breaker. I will then protect the circuit with a GFCI outlet. I am familiar with...

Replacing Circuit Breaker with Higher AMP Breaker [ 8 Answers ]

Excuse me, I did look at the code book as is suggested in your Sticky. The NFPA may answer this question, but I am not knowledgeable enough to recognize it: Our offices are upstairs in an older (renovated home) building with modern wiring. We have 4 computers, 3 printers, and miscellaneous with...

New 15A breaker trips main 100A breaker [ 6 Answers ]

Hi, I've been finishing my basement and I added a few 15A breakers One room has 8 outlets in series with the first starting about 6 feet from the main panel. There is currently no load on this outlets. When installing the drywall I accidentally shorted the outlet closest to the panel. It...

Replacing a circuit breaker with a GFI breaker- q on neutrals [ 1 Answers ]

In process on installing withquestion on neutral wires. Do you take the neutrals out of the in the main panel neutral and put them in into the breaker where its labelled "load neutral terminal" and only have the neutral "pig tail" to the panel neutral bar? Thanks!


View more questions Search