    Can a breaker cause a "bad connection" but not trip?
    I bought a new hot water heater last month and when the guy installed it and switched on the power, he said it didn't immediately work (second try it worked).. that maybe there was a breaker problem... now it's been a month and every now and then there isn't enough hot water... it has never run out but is only luke warm sometimes. The next day it might be hot again though. Or not. There seems to be no rhyme or reason to it. The guy who installed it says the problem is the breaker switch. Is that possible? It has never tripped the breaker... can there be a "bad connection" at the breaker but not bad enough to trip it? Is this something that an electrician would fix or is it something the hot water heater installer guy would fix? Or does it sound like a problem with the hot water heater installation... please advise. Thanks.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Dec 28, 2007, 02:38 PM
    A loose connection or a defective breaker will not necessarily cause a breaker to trip.

    Yes, an electrician should be called in to check and repair any loose connections in the panel or replace the breaker. Ask him to check the entire water heater circuit for any other problems, as the loose connection can be anywhere in the circuit. A good electrician will be able to check the water heater for proper operation.

    If there is any problem found with the water heater, then that contractor can be called in to fix that problem under warranty. If there was no electrical problem found, then he should foot the bill for the electrician.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Circuit breaker with "10kA 120/240v~" and a yellow D [ 6 Answers ]

I just bought a old place with very poor upkeep. The circuit breakers weren't labeled at all. I went To label all of them and was able to determine all Except for 2 that don't appear to go to anything. Those 2 look different than the rest and I was Wondering what they might be for. They...

Honda accord 2000 6 cyl " the light "check" is on" [ 1 Answers ]

My honda accord 2000 6 cyl. With 101000k miles is was with the light "check" on. I took To a non-honda mechanic and he erased it. The computer said that the code is PO700, and the mechanic said that it needs to have the "transmission rebuilt", and the price ranges from $ 1500.00 - 1600.00. My...

"lose" dsl connection [ 1 Answers ]

When I use ie7 on the web all is OK. If I don't use the connection for some time it will not connect to any page. Dsl still on. I have to reboot to use the web again. I know the dsl connection is OK and running because I am still using it with another program (no conflicts) Dave

OPT "business trip" deduction [ 1 Answers ]

Hello, I am a student working under F-1 OPT and expecting an H-1 soon. I heard that while working under OPT, I am allowed to treat it as an "extended business trip", meaning that the housing/food/transportation expenses during this period are not taxable. Is this true? If so, where is the...

Tstat wiring - dual transformer, 1 "R" connection [ 1 Answers ]

I have a dual transformer system - one for heat, one for cool. The Thermostat I'm replacing has an Rc and an Rh connection. The new Thermostat has a single R connection. The transformers are in phase With each other, however, the heat one puts out 24vac, while the Cooling one is at 26.7vac. Can...


View more questions Search