    Service grounding
    I have a 200 amp 2 family meter pan, with 2 100amp panels located in the basement right behind the meters. If I run a #6 stranded ground wire to 2 ground rods and hook it up in one of the panels and install a jumper to the other panel, and run a #4 to the water main and hook it up at the meter pan, is this correct? The two 100 amp panels are being powered by 100 amp SEU. They do not have an insulated neutral, I do not think that they need one. Is that right? Thank you.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jul 30, 2008, 01:37 PM
    Do not do as you proposed at the panelboards, no need to.

    Assuming you have a 2 gang ( 2 position) meter pack, 200 amp rated with two 100 amp sockets, you should find a small lug along with the two large lugs for the neutrals. This lug is specifically for the #6 grounding electrode conductor.

    SEU cable is fine from the meter to the panelboard, since the Main Breakers are in the panels.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

200 amp service / grounding [ 3 Answers ]

I have a 200 amp meter on a power company pole in the country for barn electricity. I have built a small shed 285' away and want 100 amp service. Based on the distance, I am planning on using 4/0 4/0 2/0 Al URD cable in 2" conduit buried 24". To get the lug sizes to fit the 4/0, I am using 200...

2 family service grounding [ 7 Answers ]

For a 200 amp 2 family overhead service I am using a primary and a secondary ground. A #6 stranded copper to two ground rods and a #4 stranded copper to the water meter. My question is, do I run the ground wires to the meter bank or to the panels? I believe it is the meter bank but just want to...

Grounding connection in service panel [ 3 Answers ]

I'm presently having problems with electrical in floor heat GFCI tripping in various circuits. This is a new installation. I can't measure any grounds on any of these circuits. I checked the main panel and I can't find a bonding strap or conductor between the neutral and the grounding bar in the...

Grounding for 400 amp service [ 1 Answers ]

How to ground 400 amp service with 2 200 amp panels one on disconnect switch

Proper grounding for 400A service and adjoining panel [ 1 Answers ]

I am installing a 400A service panel on the outside wall of a garage. For the time being it will only be supplying power to a 125A panel located on the inside wall of that garage. The 125A panel will be mounted inside the wall directly behind the 400A service, and the two will be connected by...


View more questions Search