    Grounding for 400 amp service
    How to ground 400 amp service with 2 200 amp panels one on disconnect switch
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Oct 21, 2007, 04:58 AM
    At the main disconnect, is where the incoming Line neutral, the two neutrals going to the two panels, the two equipment grounding conductors, and the grounding electrode conductor all connect at one large multi-port lug.

    The grounding electrode conductor will connect to a grounding electrode. If you have city water, or well water, with at least 10 feet of metal pipe in the ground, this will be your primary electrode. To this add at least one supplemental ground rod. With this method, you need to use #1/0 copper wire to the water and then to the ground rod.

    If you don't have metallic water line to use as a grounding electrode, you then need to use at least one ground rod, most local codes require two rods, and with this method you can use a min of #6 copper wire to both rods.

    Any connection between grounding electrodes must be continuous wire, no breaks or splices.

    Be sure to use the insulated neutral bar in each panel for neutrals only, and add equipment ground bar bolted directly to the panel metal box using machine thread screws, for bare or green equipment grounding conductors only.

    Do not install a bonding jumper at the neutral bars in the panels, keeping the neutral bar insulated and isolated from the metal box.

    If you use the ground rod method, you need to "bond" any metal pipe system in the home with min #6 copper wire to the equipment ground bar.

    I know, too many "if's". There are too many scenarios to address without knowing the specifics of your installation.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

400 amp service, 2 200 amp panels, 320 amp meter socket [ 10 Answers ]

Hi, this is my first post here, but I have been reading a lot and have already learned a bunch. I want to thank TK already and hope you reply to this. I am in the process of designing my electrical system for my new home. I have some electrical experience, but am by no means a pro. I am...

400 amp service with 2-200 amp panels & 320 amp socket [ 6 Answers ]

Hi TK. I am running 400 amp service into my new contruction home. The electric compnay is running a single 400 amp line to the meter. I have to split it to the two panels at that point. You had told me once before that I need a 320 amp meter socket and then run 2-200 amp lines to the separate...

400 amp service [ 1 Answers ]

I need a diagram of what a typical power pole to detached garage the to house service looks like making a 200 amp service in each building

400 amp service for home [ 2 Answers ]

I'm building a home and want to have 400 amp service. I understand the way this is done is by running (2) 200 amp panels in the house. My service provider asked me for a riser diagram for this service. I'm not sure how to draw this? Can you help?

New Home 400 amp service [ 3 Answers ]

I brought in 400 amp to my outside meter for my new log home. I had planned to split off 200 to the house and 200 to a future shop. However I don't think 200 will be enough from time to time. One expert I asked said I would be running at 600 AMP requirement. I think he is nuts. The main thing...


View more questions Search