    Main breaker keeps tripping
    We have a challenger 200 amp 240V main service panel. It was installed as new construction in nov. or dec. of 90'. The main breaker has started to trip off on occasion and we have to stumble around and get to the panel to reset it. I was told the breaker was discontinued a long time ago. What is a guy to do??
    smearcase's Avatar
    smearcase Posts: 2,392, Reputation: 316
    Ultra Member
     
    #2

    May 12, 2008, 05:10 PM
    Assuming there have been no modifications to the panel, I don't know why the main breaker would have been "discontinued" and if it is tripping it is obviously hooked up.
    The main breaker could be malfunctioning or it may simply be doing its job--that is tripping because more than 200 amps are being drawn by your home circuits, which can occur even if none of the individual breakers trip. Other wiring and/or bad breakers in the main panel could also trip the main breaker. Assuming the main breaker can normally be reset without your having to turn some appliances off first, it could be a bad main breaker or a short or defective branch circuit breaker in the main panel. I am not a licensed electrician.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    May 12, 2008, 05:47 PM
    Main breakers rarely fail on their own. There is a better chance the panel itself is causing it to trip. A bad or burned buss is likely the culprit.

    This is typically NOT something a DIY can take care of. I would call an electrician out to check it.
    Wandasueme's Avatar
    Wandasueme Posts: 4, Reputation: 1
    New Member
     
    #4

    May 14, 2008, 07:41 AM
    Electrician believes only aluminum wire used in house from meter box to main panel was not tight. He racked down on the nuts holding the feed from outside to the breaker, charged us $95 and went home. No problems since. Said we should have been tightening these since we built the house 17 years ago. Aren't those nuts hot?

    Thanks... Bo Whalen
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #5

    May 14, 2008, 08:54 AM
    Yep. And that's why you pay a professional to do it. A misguided screwdriver can fly off and get really hot fast.

    A more comprehensive/expensive repair could have been done at significantly more cost.
    Remove meter or have it removed. Remove and clean wires. Apply anti-oxidizing paste on wires. Use Loctite 222 on threads. Have meter put back and have the seal put back on.

    Locktite 222 is a low strength threadlocker. It works wonders.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Breaker keeps tripping [ 24 Answers ]

I need to figure this out. I have two 15 amp space heaters in my garage and when I turn them both on it throws the breaker. The breaker at box for this is rated at 20amps. I have been told that I can run both on high and won't throw the breaker. I also replaced the old breaker with a new one (same...

Difference between Main Lug and Main Breaker Panel [ 8 Answers ]

What is the difference between a Main Breaker Panel and a Main Lug Panel and can either be used in new residential construction.

Load Center Main Lug or Main Breaker for the Attic [ 5 Answers ]

I have a large attic (on 3rd floor), 38'x28', which is unfinished space. The 2nd floor central air-condition is located there and used to be fed by a 60 feet of 12/3 cable (I changed the cable to 10/3 to reduce the chance of voltage drop) and it's fed by a dual 15A breaker (240v breaker) in the...

Can I convert a main breaker Cutler Hammer loadcenter to main lug? [ 1 Answers ]

I was wondering if Cutler Hammer made a part to convert a main breaker load center (CH) style, to a main lug panel. If so, does anyone know the part number or can you refer me to a location where I could find it? Cutler Hammer's website is not too user friendly. Thanks

New 15A breaker trips main 100A breaker [ 6 Answers ]

Hi, I've been finishing my basement and I added a few 15A breakers One room has 8 outlets in series with the first starting about 6 feet from the main panel. There is currently no load on this outlets. When installing the drywall I accidentally shorted the outlet closest to the panel. It...


View more questions Search