    Wire type for a sub-panel to be installed in utility room in basement
    I would like to install a sub-panel in the basement, in our utility room. I am planning to install a 70A dual pole fuse in the main panel to feed the sub-panel. My main is 200A service, with single phase, residential, single family home. My load calculations is under 100A for the main. My new sub-panel box is rated at 150A with CU bus bar. I would be running 25 feet feed from the main to the sub-panel (via the 70A 240v dual pole fuse).

    Our local electrical supply store sells CU romax NM-B cables with all sorts of sizes. They sell size #6/3 with Ground, #4/3 with Ground, #2/3 with Ground to name a few.

    They also sell CU #3/3 with ground which is XHHW, SER, 90 oC.

    I like these cables over individual cables. Since individual cables must be run through a conduit. These cables allow me to omit the conduit, and then I can simply drill through the joist for neater and easier installation.

    Question1 - the basement and utility room (contains heating system, water heater, oil tank, etc) in the basement is considered as a dry location ?

    Question2 - is romas NM-B size #4/3 W/G (or I prefer size #2/3 W/G for future expansion) be OK to connect the main to the sub-panel ? I know these sizes are overkill for now, but I would like future expansion without having to change the wire later. I am willing to
    pay the extra cost for the 25 feet total length I need.

    Question3 - By using the NM-B (say size #2/3 W/G), would I need to worry about cable heat? I recall, seeing 90 oC rating on the store's #3/3 W/G XHHW SER wire. I noticed that their NM-B #2/3 cable didn't mention anything about temperature ratings.

    Question4 - Why the #3/3 XHHW SER cable had the temp listed on the cable, and the NM-B #2/3 cable doesn't have temp listed?

    Question5 - What does temperature really mean? Is it the melting point of the wire insulation, if the wire gets overloaded, or is it the temperature of the surrounding, where the cable is installed? 90 oC = 194 oF.

    Thanks
    -been
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    May 5, 2008, 03:47 AM
    1) Yes, your basement is considered a DRY location.

    2) I would use the 4/3 and a 90 or 100 amp sub-feed breaker. I do not buy the "future expansion" mentality. Do it that way now. Using larger wire (or a smaller breaker) makes no sense in most cases.

    3, 4, 5) You do not need to worry about heat or the heat rating of the cable. As long as you don't run the cable against a furnace flue for instance, which is common sense, you are fine.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire type from main panel to adjacent subpanel [ 1 Answers ]

I have a 200 amp main panel that is nearly full and I plan on adding a 100 amp subpanel close by in the basement of my residence (south-east PA). I happen to have some wire available that I believe is adequate gauge (based on reading many other posts) but I want to make sure the specific wire I...

Smell in utility room [ 4 Answers ]

Over the last two months we have had a rotten smell coming out of our utility room. We know it is not our drier or our washing machine and there are no leaks around any of the connecting pipes. We have also checked the u-bend under the sink as well as the dishwasher outlet pipe and are mystified. A...

Utility room backs up from Washer [ 1 Answers ]

I have a 3 year old house in the suburbs with city sewer. My Washer is above my basement. The drain hose goes into the sink next to it. When the washer discharges, it create a flood in the utility room below from the drain. When I fill the sink with regular faucet water and drain it it does not...

Wire size for Outlets in basement family room [ 6 Answers ]

I am finally getting around to doing our family room in the basement. I was wondering what size wire to pull for the outlets should I use 12/2 with ground or 14/2 with ground. Also putting in recess lights should I use 12/2 with ground for them or 14/2 with ground. Thanks T

Utility room conversion into a bathroom [ 2 Answers ]

I am considering a conversion of my utility room into a pool side bathroom and flipping the W/D to the opposite wall. Can a washer, toilet, shower, and sink run off the existing sewer and vent pipe? Additionally, my house is built on slab foundation.


View more questions Search