    Wire type from main panel to adjacent subpanel
    I have a 200 amp main panel that is nearly full and I plan on adding a 100 amp subpanel close by in the basement of my residence (south-east PA). I happen to have some wire available that I believe is adequate gauge (based on reading many other posts) but I want to make sure the specific wire I have is reasonable to use. The wire I have is 3 individual copper wires labeled: “54488 2AWG 600V MTW OR THHN OR GASOLINE & OIL RESISTANT OR AWM (UL)” plus one green ground wire labeled “8AWG TYPE THW 600V VINYL THERM CERRO-VW-1 (UL)”. Is this adequate to connect from the main panel with a new 100amp breaker added to a subpanel which has a 100 amp main breaker. The three main conductors of this wire all have black insulation – is it acceptable to use colored electrical tape to mark the white and red lines? Since these are individual conductors and even though the panels are just a few feet apart in the basement , I’m guessing I still need to use conduit. Correct? Which type(s) are acceptable (PVC, metal, flex, etc)?

    If this wire isn’t reasonable to use in this application, I will probably scale back to a 60amp breaker in the main panel and use an easier to get appropriate gauge copper wiring. The subpanel is there to handle additional new outlet and light circuits for my basement and sunroom that won’t fit in the main panel.

    Thanks in advance for your guidance.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Feb 2, 2008, 05:34 PM
    The wire size you have is fine for 100 amp. Colored tape is acceptable to mark wires. All the conduits you mention are acceptable, use the one that fits and installs the best for your situation.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How to add 300 a subpanel to 2oo a main panel [ 4 Answers ]

How do you add a 300a subpanel from a 200 a main panel to install tankless water heater

Wire type subpanel inside/outside [ 16 Answers ]

I have a detached garage I want to run a 100amp subpanel. The total wire length from main to subpanel should be less than 90ft(garage is about 50 ft away from house). I have to run from the main panel across part of the unfinished area of the basement to the cloesest exterior wall and then trench...

Convert Main Panel to Subpanel? [ 3 Answers ]

After rough-wiring my old house to a new 200 amp Main Panel (wired-in but not yet connected to the service line and still using the original 100 amp fuse-type panel) I've decided to build a major addition that makes the originally planned service entrance a poor location. Question: Can I...

Main panel as subpanel [ 2 Answers ]

Hello: I stumbled across your forum and found a question that was close to mine, but have a more detailed query. I am wiring a shop/apartment. The building has a 200 amp service panel. The main loads (a/c, range) and dedicated loads (fridge, smoke detectors, etc) are branch circuits on the main...

Subpanel or main service panel? [ 4 Answers ]

Hello, I want to put a subpanel in my shop, and was wondering if a main service panel that they sell at say Home Depot is the same thing as a subpanel? I have a 200 amp service to my house, and want to put a 100 amp subpanel in my shop. Does the term "subpanel" just mean that it is wired off the...


View more questions Search