    Modifiying service entrance
    I am in the process of building a new addition and attached garage.

    I currently have 200 amp service 4/0 alum. 100 feet UG from house to (my) pole in 2" conduit. It then crosses the street to utility owned pole, approximately 125 feet OH. (dashed yellow line)

    I would like to remove the existing pole as it impacts the relocated driveway. I would either replace entrance wire to a utility owned pole on the property line (left side of picture) or extend the exsiting 4/0 alum to this pole. I perfer the latter so I don't have to tear up my lawn, plantings, driveway and I will not need as much wire. Can I splice 4/0 alum underground? (green line). The new wire would be 225 feet UG to the pole on my side of the street and approximately an additional 125 feet acoss the street to the pole with the transformer. Is this too far? What is the max distance for 4/0 alum?

    Should I consider installing a new main panel in the garage (red line) and use my old service panel in the house
    As a subpanel? This may make sense as I will be removing the old detached garage and the wire from the house-garage and garage-barn.

    Can I splice into the exisitng wire leading from the house to the garge and reroute it over to the barn.

    Sorry if this was long winded
    Attached Images
     
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Dec 18, 2006, 01:15 PM
    I like the idea with the red line.

    Have you contacted the utility company about your proposed plan? They may have something to say about this as each utility has their own requirements.

    Splicing underground wires is always a challenge, esp if the splices will be buried. If this needs to be spliced, and yes it is possible, I would use a handhole at the splices so that they are always accessible and can be better protected.

    Sizing this feeder will depend on the utility, if they own it or if you own it, and the connected load. The calcs I did based upon a fully loaded 200 amp service, assuming the max of 80%, shows that 250 MCM aluminum wire is needed.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Service entrance cable [ 23 Answers ]

I am re-wiring an old house. It is a small 2 bedroom, 1 bath house. We put in a 200 amp service and need to run a service entrance cable about 20 -25 ft to the inside breaker panel. My question is how big of a gauge wire should we run for the service entance cable. #? 3 conductor with ground in...

Service entrance cable [ 2 Answers ]

Having new 100amp meter installed professionally,but I am burying wire to the building which is 125' from where meter is mounted. Will I have to upsize the size of wire because of the distance? I also intend to enclose in conduit, so I'm not worried about using "U" coded wire

300' run of service entrance [ 4 Answers ]

My electrician and the power co. have both agreed that 2/0 urd aluminum is sufficient for a 100 amp service for a mobile home. The run is 300'. There is a 100 amp disconnect outside and inside the mobile home. Is the acceptable? I'm just double checking their wisdom in this matter. Thanks in...

4 wire home service entrance wire size [ 1 Answers ]

Mobile home requires 4 wire electrical service entrance wire. Distance is 160 foot from meter to breaker panel. 220V service. What size wire do I use? Can I use diff. size for neutral and ground?

Service entrance [ 5 Answers ]

Can someone tell me how to find out what the amp rating of a service to a house is . The fuse box is old with edison base fuses, but the weather head and pipe to the meter cradel looks newer want to change to beaker panel Not sure what size


View more questions Search