    Electrical troblelshotting with residential condenser
    Hi,

    Need some guidance. Air handler works fine but contactors will not pull down the condensing unit.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    May 13, 2007, 10:20 AM
    You need a 24 volt signal circuit to activate the contactor in the outside unit. Start at the outside unit at the contactor and trace back to the inside to the air handler to find the defective part.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #3

    May 13, 2007, 12:06 PM
    Transformer in ir Handler Converts 240 volts to 24 v. goes to thermostat(RED)
    When set to cool RED touches Green for fan relay, and Blue out to compressor contactor.
    If when set to cool, No 24 volts at contactor coil.
    Then Go inside air Handler and troubleshoot from there.
    24 volts should be present at secondary side of transformer, No matter what thermostat set to.
    Transformer Fuse?
    JackT's Avatar
    JackT Posts: 260, Reputation: 19
    Full Member
     
    #4

    May 13, 2007, 04:22 PM
    Don't go by the color code, not everyone uses the same thing, most will use the yellow wire that should be connected to the Y terminal. As hvac1000 said, start outside and work backwards until you have 24 volts. Most likely if it was a fuse or transformer problem, the air handler blower wouldn't come on at all.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #5

    May 13, 2007, 07:05 PM
    Like JackT says.
    I wrote blue, meant yellow, Thanks, also with air handler kicking in, transformer is good.
    I will come back after recovering from flu.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Rheem RACB-030JAS residential A/C unit condenser fan motor replaced [ 26 Answers ]

I just replaced the condenser fan motor and it initially spun up then stopped, after 10 minutes it ran again then stopped. Now I can hear it buzz then stop but not spin. The original motor was a GE 5KCP39BG K075CS 1/6 HP 1075 RPM 208/230 V its replacement a Dayton 4M205G 1/4 hp 1075 RPM ...

Safer residential service. [ 3 Answers ]

Which is safer L1-110 L2-110 With center tap to ground Or L1-220 L2 gounded Thanks

Residential electricle [ 4 Answers ]

What decade was aluminum wiring installed on the interior of the house and what does it look like on the outer shieth. Allso what are your thoughts on the stuff. My family and I Are house shopping. Concerned shopper

A/c residential [ 4 Answers ]

Last summer when we had the really hot days of 90-100 degree temp outside my a/c system would not cool the house below 80 degrees inside and the unit would run constantly I decided today to check the system I put my guages on the cond. Unit and had a suction pressure of 45 and a discharg pressure...

Replacing A/C - condenser or heat pump/condenser [ 1 Answers ]

I live in a condo. All of the units in the building need to new air conditioners because they are all old and will not survive a scheduled reroofing of the building. The association got a bid for a company that will put in a new condenser unit for anyone who wants one - it is about $1500 installed....


View more questions Search