    Raptor_x's Avatar
    Raptor_x Posts: 5, Reputation: 1
    New Member
     
    #1

    Apr 20, 2005, 09:13 PM
    Basement Vent Question
    I was trying to layout a basement bathroom for a new construction home. Please view the attached file to see a schematic. I would like to place a vent behind the sink, and next to the bath. I'm not sure if this is adequate for the toilet placed between them. I was going to place the vent between the toilet and the bath, but the footer for my basement is in my way. Any suggestions will be appreciated.

    Thanks,

    Dan
    Attached Images
     
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #2

    Apr 21, 2005, 06:22 AM
    Basement Vent Question
    Quote Originally Posted by Raptor_x
    I was trying to layout a basement bathroom for a new construction home. Please view the attached file to see a schematic. I would like to place a vent behind the sink, and next to the bath. I'm not sure if this is adequate for the toilet placed between them. I was going to place the vent between the toilet and the bath, but the footer for my basement is in my way. Any suggestions will be appreciated.

    Thanks,

    Dan

    Good morning Dan,

    Nice job of drafting up the print. However you're discharging a major fixture, (toilet) past a unvented minor one,(bath) and that's against code.
    You MUST run a vent off the lavatory, in addition the holding tank must be vented also but you may tie the two vents together in the basement and run them out as one vent. As for the tub let me give you a few options.
    (1) You may tie the tub in between the toilet and the lavatory and be wet vented.
    (2) You may tie the lavatory in ahead of the toilet and tie the tub drain to the lavatory drain and wet vent the tub that way.
    (3) You may keep the present lay out and install a mechanical spring loaded vent just after the tub trap. This vent does not need to be piped to the outside.
    My vote goes for door #3.
    If you need more information on mechanical vents click on back.
    Good luck, Tom
    Raptor_x's Avatar
    Raptor_x Posts: 5, Reputation: 1
    New Member
     
    #3

    Apr 21, 2005, 06:56 AM
    Thanks for the help. Any information you could give me on the mechanical spring loaded vent would be appreciated. I've attached the sketch with a minor modification made in blue. If I changed the tub drain so it ties into the main drain after the vent in the south wall, would this change make the venting acceptable? Then I would have a vent at the lavatory through the north wall, and a vent between the tub and toilet in the south wall. I plan on running a 2" vent, and I will be within 5 feet of the toilet.

    Thanks again for the help.

    Dan
    Attached Images
     
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #4

    Apr 21, 2005, 12:31 PM
    Quote Originally Posted by Raptor_x
    Thanks for the help. Any information you could give me on the mechanical spring loaded vent would be appreciated. I've attached the sketch with a minor modification made in blue. If I changed the tub drain so it ties into the main drain after the vent in the south wall, would this change make the venting acceptable? Then I would have a vent at the lavatory through the north wall, and a vent between the tub and toilet in the south wall. I plan on running a 2" vent, and I will be within 5 feet of the toilet.

    Thanks again for the help.

    Dan
    Hey Dan, your tub is now vented in code. Looks good to me. Congratulations, Tom

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Basement return air vent [ 2 Answers ]

Carrier, modal 58MAC120-20, direct air forced air furnace, seven years old in a 2,700 square foot home seven years old. The basement is 1,200 square feet, open and half finished, has two supply air regesters and no return air vent. What size "opening" is recommended for this area?

Basement shower drain vent? [ 1 Answers ]

I am installing a basement shower which was stubbed when the floor was poured. A P trap is in the floor about 3' from the main horizontal sanitary line which goes out to the septic. I can see no vent lines and wonder if I need to vent the shower. If I do need to vent it, the vent needs to...

Basement Bathroom Vent [ 6 Answers ]

I am finishing my basement. It has roughed-in plumbing under the slab for a bathtub, sink and toilet tied to pit for a sewage ejector pump to pump up to the municipal sewer. There is a 2" capped PVC pipe protruding from the first floor bathroom, which is directly above this bathroom. I am...

Basement wet-bar vent [ 2 Answers ]

My basement is finished w/ 1/2 bath & wet bar. Bathroom sink drains to the rough-in meant for shower drain (long story). On other side of wall, wet bar drains into the same drain as the bathroom sink. Both sinks have their own p-traps (plus the rough-in trap under concrete), but neither has...

Basement bathroom vent [ 5 Answers ]

I want to put a shower, sink and toilet in a basement I am developing. When they built the house they did not rough in any plumbing nor did they run a vent to the basement. After I break up the concrete to install the drains I still have the venting problems. Can I run a vent line horizontally out...


View more questions Search