                      Apr 12, 2005, 07:37 AM
                  
                 |  |  
  
    | 
        
        
        
       
        
        Doubling up wire
       
                  
        Wondered how the NEC feels about using parallel feeders instead of footing the cost for more expensive larger sized wire? Application is UF-B from house to detached garage. Want to use 2 sets 12-3, WG instead of paying for 10-3 WG (or 8-3 WG). Am not interested in having an inspection.
     |  
    |  |  
	
		
	
	
  | 
    
      
                |  | Uber Member |  | 
 
                  
                      Apr 12, 2005, 08:59 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        I can't give you what code says.  I do know it is quite common to use multiple wires to carry large industrial 3 phase loads.  I have seen things like 3 conduits each carrying three 500 MCM singles.  They are quite common in factories.
     |  
    |  |  
	
		
	
	
  | 
    
      
                |  | Full Member |  | 
 
                  
                      Apr 12, 2005, 09:35 AM
                  
                 |  |  
  
    | 
        
        
        
       
        
        I guess... 
       
                  
        
	
		
			
			
				
					  Originally Posted by labman I can't give you what code says.  I do know it is quite common to use multiple wires to carry large industrial 3 phase loads.  I have seen things like 3 conduits each carrying three 500 MCM singles.  They are quite common in factories. ... it would be a better bet to place them in PVC conduit so if they ever are found to violate code, they can be replaced easier. You agree, Labman?
     |  
    |  |  
	
		
	
	
  | 
    
      
                |  | Uber Member |  | 
 
                  
                      Apr 12, 2005, 11:54 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Certainly wouldn't hurt.  Do you already have a big coil of 12-2?   Again you buy 2 lengths of it plus the conduit, surely one length of 10-2 would be cheaper.  Also if you run conduit, you could run singles rather than cable.  Stranded singles pull easier than solid cable.
     |  
    |  |  
	
		
	
	
  | 
    
      
                |  | Uber Member |  | 
 
                  
                      Apr 13, 2005, 01:00 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Per the current edition of the National Electric Code:
 "Section 310.4 Conductors in Parallel.
 Aluminum, copper-clad aluminum, or copper conductors of size 1/0 AWG and larger, comprising each phase, neutral, or grounded circuit conductor, shall be permitted to be connected in parallel (electrically joined at both ends to form a single conductor)."
 
 Should you install electric wiring without proper licenses or permits, and loss of life and/or property occurs due to improper installation, you insurance will not cover your losses.
 
 Something to consider.. save a few bucks now, and pay large bucks later.
 |  
    |  |  
	
		
	
	
  | 
    
      
                |  | Full Member |  | 
 
                  
                      Apr 13, 2005, 07:53 PM
                  
                 |  |  
  
    | 
        
        
        
       
        
        Thanks for the... 
       
                  
        
	
		
			
			
				
					  Originally Posted by tkrussell Per the current edition of the National Electric Code:
 "Section 310.4 Conductors in Parallel.
 Aluminum, copper-clad aluminum, or copper conductors of size 1/0 AWG and larger, comprising each phase, neutral, or grounded circuit conductor, shall be permitted to be connected in parallel (electrically joined at both ends to form a single conductor)."
 
 Should you install electric wiring without proper licenses or permits, and loss of life and/or property occurs due to improper installation, you insurance will not cover your losses.
 
 Something to consider..save a few bucks now, and pay large bucks later.
 ... info and the reminder of just how dangerous electricity is!
     |  
    |  |  
 
 
 
  
    | Question Tools | Search this Question |  
    |  |  |  
 Add your answer here.
 
Check out some similar questions!
Neutral wire is hot(has voltage potential like the black wire)
 [ 5 Answers ]
Hi, 
 
   The problem started at midnight last week. One of my line in the basement is starting to have issue whenever I connect a water pump or appliances to the outlets. Before I plug the appliance in, the neutral is neutral(zero voltage), but when I plug the appliance in, the neutral is now...
 
3-wire home, 3-wire fan, 2-wire remote
 [ 9 Answers ]
Greetings, 
My home is 3-wire. I bought a Hunter ceiling fan (model 23811). The fan came with a remote assy. That I do NOT want to use...  
 
The fan has standard 3-wire connections (black, white, blk&white strip, ground). The remote receiver home-side wiring looks to be for 2-wire (blk and white)....
 
4 wire home service entrance wire size
 [ 1 Answers ]
Mobile home requires 4 wire electrical service entrance wire.  Distance is 160 foot from  meter to breaker panel.  220V service.  What size wire do I use?  Can I use diff. size for neutral and ground?
 
2 Wire White-Rogers with no wallplate wire question
 [ 2 Answers ]
Hi there.  
 
I want to replace my current White-Rogers 1E56W309 thermostat with a new Honeywell RTH7500D. The problem is that the tools that installed my high efficiency furnace didn't install the wall plate with my thermostat (it was a new house and the builder contracted these guys). Instead,...
 View more  questions
Search
 
 |