  • Apr 12, 2005, 07:37 AM
    Flickit
    Doubling up wire
    Wondered how the NEC feels about using parallel feeders instead of footing the cost for more expensive larger sized wire? Application is UF-B from house to detached garage. Want to use 2 sets 12-3, WG instead of paying for 10-3 WG (or 8-3 WG). Am not interested in having an inspection.
  • Apr 12, 2005, 08:59 AM
    labman
    I can't give you what code says. I do know it is quite common to use multiple wires to carry large industrial 3 phase loads. I have seen things like 3 conduits each carrying three 500 MCM singles. They are quite common in factories.
  • Apr 12, 2005, 09:35 AM
    Flickit
    I guess...
    Quote:

    Originally Posted by labman
    I can't give you what code says. I do know it is quite common to use multiple wires to carry large industrial 3 phase loads. I have seen things like 3 conduits each carrying three 500 MCM singles. They are quite common in factories.

    ... it would be a better bet to place them in PVC conduit so if they ever are found to violate code, they can be replaced easier. You agree, Labman?
  • Apr 12, 2005, 11:54 AM
    labman
    Certainly wouldn't hurt. Do you already have a big coil of 12-2? Again you buy 2 lengths of it plus the conduit, surely one length of 10-2 would be cheaper. Also if you run conduit, you could run singles rather than cable. Stranded singles pull easier than solid cable.
  • Apr 13, 2005, 01:00 PM
    tkrussell
    Per the current edition of the National Electric Code:

    "Section 310.4 Conductors in Parallel.
    Aluminum, copper-clad aluminum, or copper conductors of size 1/0 AWG and larger, comprising each phase, neutral, or grounded circuit conductor, shall be permitted to be connected in parallel (electrically joined at both ends to form a single conductor)."

    Should you install electric wiring without proper licenses or permits, and loss of life and/or property occurs due to improper installation, you insurance will not cover your losses.

    Something to consider.. save a few bucks now, and pay large bucks later.
  • Apr 13, 2005, 07:53 PM
    Flickit
    Thanks for the...
    Quote:

    Originally Posted by tkrussell
    Per the current edition of the National Electric Code:

    "Section 310.4 Conductors in Parallel.
    Aluminum, copper-clad aluminum, or copper conductors of size 1/0 AWG and larger, comprising each phase, neutral, or grounded circuit conductor, shall be permitted to be connected in parallel (electrically joined at both ends to form a single conductor)."

    Should you install electric wiring without proper licenses or permits, and loss of life and/or property occurs due to improper installation, you insurance will not cover your losses.

    Something to consider..save a few bucks now, and pay large bucks later.

    ... info and the reminder of just how dangerous electricity is!