    120 amp sub-panel
    My home was constructed in 1996 and has a CH 200 amp main panel with all available slots filled. In the past several years I have added service to my garage (20 amp, light load) which involved replacing a single breaker with a dual. I also replaced our 240v electric cook top with a gas unit which should have lighttened the total household load considerably.

    I want to install a Watts Premier tankless water heater which requires 4 - 30 amp circuits. I plan to do this through the installation of a sub-panel. Since my main panel is full I plan to remove the two existing double 40 amp breakers (80 amps total) used for the dual air conditioner units in the main panel with larger breakers to feed the sub-panel and then move the air conditioner breakers to the sub-panel. This would mean a 200 amp sub-panel, is this possible or I am over loading the main feed? Can I feed the sub-panel some other way without installing new breakers in the main?

    Thanks
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Apr 16, 2007, 12:26 PM
    Really need to confirm your 200 amp service can handle the load of this water heater. According to the specs I found, the max amp draw will be 116 amps, and this must be calculated at 100 %.

    Your air conditioner will also need to be assumed at running full load, and with the water heater.

    If you provide,
    Total square footage of livable space,
    List of all major electric appliances.
    Total KW or amp load of AC

    I can do the service sizing calculations. My intuition is your service cannot handle this added load.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

200 amp panel feeding a 100 amp panel roughly 130' away [ 7 Answers ]

Hi all, We are building a apartment above the garage,my question is what size wire do I need to run from the 200 amp panel to the 100 amp panel roughly 130' away? I want to use aluminum wire as I think copper would be to costly. Thanks for your help in advance, Dude :eek:

60 Amp Panel.how many breakers? [ 2 Answers ]

I recently bought a house with an old Federal Pacific Panel in it. (Yes yes I know, major fire hazard.) I was just wondering, it is rated as a 60 amp panel, does that mean that the sum of all the breakers must be less than 60 amps, or that no one breaker can exceed 60 amps?

200 Amp Service Panel with 60 Amp Main Breakers [ 26 Answers ]

I was told when we purchased our house that it had 200 Amp service which it appears to be; however, the top of each bus bars only has 60 Amp breakers for the Main shut offs. Is this normal? Each bus bar is connected to a hot wire (one red and one black) and then the two 60 amp breakers are...

Sub panel 40 amp wiring [ 1 Answers ]

I have a 70 amp sub panel. I'm trying to figure out how to wire in a 40amp breaker in the sub from the panel in my house. I have two hot wires coming in to separate lugs, one neutral, but the breaker itself has one trip/reset lever yet has two screws on the bottom of the breaker;one on each side....

125 amp sub panel [ 5 Answers ]

What size wire do I need to pull for a 125 amp sub panel. Thank you


View more questions Search