Ask Experts Questions for FREE Help !
Ask
    Creative55's Avatar
    Creative55 Posts: 3, Reputation: 1
    New Member
     
    #1

    Apr 20, 2016, 11:40 PM
    Will my plumbing venting work
    Hello,
    I would like to install a bathroom and would like to know if my proposed plumbing diagram venting will work? The original plumber who scoped it out said I should run a 3" drain but I hear a 4" (as marked in the drawings) is what is normally used. The slope will be a 1/4 drop for every foot.

    Thank you.
    Attached Images
      
    Mike45plus's Avatar
    Mike45plus Posts: 230, Reputation: 27
    Full Member
     
    #2

    Apr 21, 2016, 04:19 AM
    Creative,
    Yes, it will work however, a 3" drain would be just fine and code compliant. The IRC and IPC do not require an individual vent for the toilet as long as there is a 3" vent stack or stack vent connected to the dwv system...
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #3

    Apr 21, 2016, 05:30 AM
    If your local code allows, use an AAV under the sink. Saves running pipe.
    Milo Dolezal's Avatar
    Milo Dolezal Posts: 7,192, Reputation: 523
    Plumbing Expert
     
    #4

    Apr 21, 2016, 06:50 PM
    Nice drawings !

    3" drain is perfectly OK... You can combine all vents into one, 2" vent, about 48" above the floor, and continue with 2" vent above roof line

    We don't use 1 1/4" vents, but 1 1/2"

    Hope that helps

    Milo
    Creative55's Avatar
    Creative55 Posts: 3, Reputation: 1
    New Member
     
    #5

    Apr 23, 2016, 09:47 AM
    Quote Originally Posted by Mike45plus View Post
    Creative,
    Yes, it will work however, a 3" drain would be just fine and code compliant. The IRC and IPC do not require an individual vent for the toilet as long as there is a 3" vent stack or stack vent connected to the dwv system...
    Thank you Mike45plus,
    Is there any advantage to running a 3 over 4 inch drain?

    Quote Originally Posted by Milo Dolezal View Post
    Nice drawings !

    3" drain is perfectly OK... You can combine all vents into one, 2" vent, about 48" above the floor, and continue with 2" vent above roof line

    We don't use 1 1/4" vents, but 1 1/2"

    Hope that helps

    Milo

    Thank you Milo, would it make things flow smoother if I used a 4 inch drain?

    Quote Originally Posted by ma0641 View Post
    If your local code allows, use an AAV under the sink. Saves running pipe.

    Thank you, what is a AAV?
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #6

    Apr 23, 2016, 10:52 AM
    "Thank you, what is a AAV?"

    Air Admittance Valve also called a Studor. In some cases it replaces a roof vent and is very useful in retro fitting and with kitchen islands. Our peninsula sink and basement bath vanity use them. They are not accepted at all locations so check with your plumbing codes.

    Milo Dolezal's Avatar
    Milo Dolezal Posts: 7,192, Reputation: 523
    Plumbing Expert
     
    #7

    Apr 23, 2016, 04:52 PM
    Creative55:

    We size pipes according to number and type of plumbing fixtures. Each plumbing fixture has assigned number of "plumbing units." In your case, you are adding toilet (3 units), sink (1 unit ), and shower (2 units ) which amounts to 6 plumbing units. So theoretically speaking, you could triple the load to max the pipe out as horizontal load for 3" pipe is 20 units / 2 toilets maximum. Moreover, 3" pipe is easier to install, fits better in tight spaces and fittings are lot cheaper than in 4" size ... However, if you do it in 4" pipe, it will be perfectly OK to do.

    Hope that explains

    Milo
    Creative55's Avatar
    Creative55 Posts: 3, Reputation: 1
    New Member
     
    #8

    Apr 24, 2016, 10:48 PM
    Quote Originally Posted by ma0641 View Post
    "Thank you, what is a AAV?"

    Air Admittance Valve also called a Studor. In some cases it replaces a roof vent and is very useful in retro fitting and with kitchen islands. Our peninsula sink and basement bath vanity use them. They are not accepted at all locations so check with your plumbing codes.

    OH... got it, thank you very much for you help.

    Quote Originally Posted by Milo Dolezal View Post
    Creative55:

    We size pipes according to number and type of plumbing fixtures. Each plumbing fixture has assigned number of "plumbing units." In your case, you are adding toilet (3 units), sink (1 unit ), and shower (2 units ) which amounts to 6 plumbing units. So theoretically speaking, you could triple the load to max the pipe out as horizontal load for 3" pipe is 20 units / 2 toilets maximum. Moreover, 3" pipe is easier to install, fits better in tight spaces and fittings are lot cheaper than in 4" size ... However, if you do it in 4" pipe, it will be perfectly OK to do.

    Hope that explains

    Milo
    Thank Milo, I wasn't aware of the assigned numbers "plumbing units" I appreciate your detailed explanation!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Plumbing venting [ 9 Answers ]

I had probs with little water in toilet bowl,and gurgles,it was suggested it was a venting prob,either outside vents were frozen or poor venting.I went to local hardware bought 2 cheater vents put one under kitchen sink,and one under bathroom sink.beforehand if I flushed toilet,tub would gurgle,if...

Plumbing venting [ 1 Answers ]

I am building a cabin and I am trying to figure out how far I can install a toilet from a 3 inch vent stack without adding a separate vent for that toilet. I have read on this site it can be 6 to 10 feet depending where you live. The cabin is located in Island County Washington State.

Venting plumbing [ 1 Answers ]

How big should the vent pipe be? Can it be too big, We're thinking of using 3inch, would that be OK? We plan to just use this one for the toile, sink and shower. Would it better if we use more than one vent? Its all going to be within feets of one another. Thanks.

Plumbing venting [ 6 Answers ]

We had a home built for us this past summer. I had a gentleman checking our furnace in Dec, and he also inspected a few other items, one of those being the attic where he saw the venting tubes, and stated to me he didn't know how this house passed the plumbing inspection.. he saw two 3"pipes...


View more questions Search