    How do I test the induction motor on a lennox g40uh
    My old furnace finally crapped out got a used Lennox g40uh furnace hooked it up and it won't turn on the 2 LEDs are slow blinking which indicates everything's normal the manual says the induction motor is supposed to come on first its no need to find out how to test it
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Nov 20, 2015, 06:59 PM
    Remove the black lead from the inducer motor at the control board. Call for heat. Measure the AC voltage from the induced spade connection to neutral spade. If you have 120VAC,and the motor is not turning, the motor is probably bad. With no voltage it is somewhere else.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #3

    Nov 20, 2015, 07:08 PM
    [QUOTE=ma0641;3754019]

    QUOTE]
    Did it run through a diagnostic purge test first? Normally, when first started up, the air handler fan will run, system checks itself and then turns off. Then, it will start cycle. Inducer, pressure switch, igniter, gas valve. Check this, remove the black lead from the inducer motor at the control board. Call for heat. Measure the AC voltage from the inducer spade connection to neutral spade. If you have 120VAC,and the motor is not turning, the motor is probably bad. With no voltage it is somewhere else.[/
    4giants's Avatar
    4giants Posts: 2, Reputation: 1
    New Member
     
    #4

    Nov 20, 2015, 07:49 PM
    The furnace didn't do the diagnostic purge self test. Both green LEDs blink slow
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #5

    Nov 21, 2015, 08:21 AM
    That is a normal code for Lenox. Did you test for voltage at the inducer when calling for heat? You have to start testing somewhere. Batteries OK in the thermostat?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Lennox G40UH running when not required [ 1 Answers ]

I have a 5 year old Lennox G40UH gas furnace. The furnace runs for short periods (2-3 minutes) 10-15 times per hour. This happens even when the house temp is above the thermostat setting. I have replaced the thermostat but the problem continues. I have checked the diagnostic lights before, during...

Lennox g40uh - delayed ignition [ 0 Answers ]

G40UH lennox is about 3 years old, the heat on message comes on , but sometimes it takes a long time before it fires up? Any suggestion of what the problem could be?

Lennox G40UH(X) series - blowing cold air outside [ 3 Answers ]

Lennox G40UH(X) series - blowing cold air outside - would like to know what I can check before having to spend money for service to come check it? Can I check filters, fans, wires, etc?

Blower does not run automatically on lennox g40uh(x) furnace [ 0 Answers ]

The thermostat sends the signal for heat and the exhaust fan goes on, but the blower fan does not start and the furnace does not ignite. The fan blower does work if I manually turn the fan to on (instead of auto) at the thermostat. I tried tapping on the limiters, but it doesn't seem to help. ...

Single-phase induction motor versus 3Phase-induction motor [ 1 Answers ]

I know the advantages of 3phase induction motor (IM) when compared with a single-phase IM one. However I need to justify using a single-phase IM (main and auxiliary windings) with a 3 legs inverter instead a 3phase IM with also a 3 legs inverter. Are the single-phase IM cheaper the 3phase one...


View more questions Search