    Tappan furnace
    False flame or gas valve relay shorted indicated on panel . My furnace will ignite for about 1-2 min then shut off . I cleaned the igniter but problem persists . Can someone help me ?
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Dec 14, 2014, 09:28 AM
    If it burns that long, you may have a high temp switch opening or a rollout switch. Make sure filters are clean and you are getting g good airflow.
    drtom4444's Avatar
    drtom4444 Posts: 3,282, Reputation: 145
    Ultra Member
     
    #3

    Dec 15, 2014, 09:16 AM
    If it is indicating that a gas valve relay is shorted then you need to trace back the wires attached (All 24 volt control wiring) to the gas valve until you find the relay. One wire will be the low voltage common at the transformer and the other one will be to the normally open contact on the relay. You will have two coil wire terminals which you should test with a meter set to "ohms" (Have the power turned off when using this function.). Read across the terminals and you should have about 200-300 ohms or so. If it is low then you have a short, but also test and see if it reads to ground. Disconnect wires when you do this test or any other test using the "ohm" function. At least one wire should be disconnected, but if you are testing to ground disconnect both wires. Then trace the coil wires back further to see where they lead. You should find a safety somewhere that is opening. You also need to test the gas valve to see if it is shorted or the coil is grounded. Test from a terminal to the body of the valve to test for a ground. If any component is grounded or shorted it is bad. Grounds are best found with the meter set to the highest range on "ohms." Here are some diagrams: https://dl.dropboxusercontent.com/u/...20Diagrams.zip

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Tappan guf 80d24 e3 furnace [ 0 Answers ]

How do you turn on a tappan guf 80d24 e3 furnace

SJC ( Tappan ) furnace no spark [ 2 Answers ]

I have an 1979 SJC ( Tappan ) intermittent ignition power vent furnace which will not light the pilot. The inducer motor runs when the thermostat calls for heat, and I have 24 V at the R & W terminals on the transformer, but nothing at the gas valve. What should I check? Thanks!

How old is my tappan furnace model GUF-80-0-34-E5 [ 1 Answers ]

It's serial # is 76 A24355

Tappan Furnace Fuses [ 0 Answers ]

I have a Tappan Furnace. I just replaced the circuit board and I am getting no power at all-no lights coming on. I do have cover replaced and I do have power on. Is there a fuse other than the circuit board fuse that might need tobe replaced? If so where do I loacate it? Thanks


View more questions Search