    200 amp main panel feeding 200 amp subpanel
    I want to run the line power from the utility pole through an underground service to a main panel on my shop, then to a 125 amp subpanel in the shop and through 70 ft of buried 2.5 in pvc conduit to a 200 amp subpanel in my house. (the shop is bettween the utility pole and house) I have a siemens MC0816B1200SCTM 250 AMP MAIN PANEL. It has a 200 amp main breaker , it has 8 stabs, the largest breaker it can take is 135 amps, which is fine for the shop, but I still need 200 for the house. The buss bars have what look like large feed through lugs at the bottom that I could use for my 200 amp subpanel in the house. The label in the panel says those lugs take from #4 through 250 kcml wire, which would work for a 200 amp subpanel, but there is nothing on the panel saying it's rated for a 200 amp feed through. Is that something I can do with this panel ? If so, at what depth would the conduit going to the need to be at ?
    Thanks, mike
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Nov 27, 2014, 05:21 AM
    That is a 200A feed-through meter/main. The lugs out the bottom on this particular panel are the feed-through lugs right off the load side of the meter. Remember, this will make the panel in the house a main panel, not a sub-panel.

    The conduit, assuming PVC, should be at least 18" to the top.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

200 amp. Main panel, fed from the meter. How do a I Install a 200 amp sub-panel [ 3 Answers ]

I have a 200 amp panel, fed from the meter located in the house. I want to add another 200 amp.sub-panel in the garage, how can I connect the two? And if so what size of wire do I use? Thank's

Main 200 amp. Installing a 200 amp sub-panel. Wire size jumper to connect(2 /100 amp) [ 1 Answers ]

Installing a 200 amp.sub-pane (type D- Hom), the main panel is 200 amp.also, I'm using 2 /100 amp. Breakers. My question is : what wire size do I need for the jumper to connect the two breakers. I'm using #2 X3 and #4 ground wire to connect the sub-panel, do I need the same#2 for the jumper? Or...

Main Cutoffs: 200 amp outside panel feeding a 200 amp inside circuit breaker panel. [ 1 Answers ]

Would you please clarify an answer you gave to a previous question? Your answer makes me wonder about the capacity of the main shut-off circuit breaker in an inside circuit breaker panel. Is the inside circuit breaker panel the same as what you call a subpanel? Here's the question and answer:...

200 amp main feeding 200 amp sub-panel [ 13 Answers ]

The utility spotter recommendeds the corner of my house as the location for a 200 amp aerial service entrance/meter base. My county requires a shut-off switch with the meter base, so a combination meterbase and load center is the standard here. I'm okay with her recommended SE location, but...

100 Amp Subpanel from 200 Amp main panel [ 2 Answers ]

I want to install a subpanel to be used to supply branch circuits to a new kitchen, laundry, garage, and some additional lighting and receptacles. The 200 amp main panel is about 50 ft away but because of the obstructions, we'll need about 85 feet of cable to connect the 100 amp subpanel. Since...


View more questions Search