    1-pole or 2-pole circuit breaker
    Hi, I want to hook up a 9.2kw stiebel eltron dhc 10-2 tankless water heater to a Square D QO electrical panel and it requires a 50A circuit breaker and 8-gauge electrical cable (3 conductors?), should I buy a 1-pole or 2-pole plug in circuit breaker? Why? What is the difference between a 1-pole and 2-pole even though both are 50A? Thank you!
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #2

    Oct 10, 2014, 07:14 AM
    You will need a double pole 50 amp breaker and 8-2 with ground cable. Granted that is three wires, two conductors and the ground wire, but the ground wire is not a conductor.
    You need a double pole breaker because the heater requires 240 volts. You get 240 volts (in USA) by connecting to the two 120V lines coming into the breaker box.

    You must use a double pole breaker, not two single pole breakers because the two 120V lines must be disconnected at the same time.

    Note 8-2 w/ground cable is not the same as 8-3 cable.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Oct 10, 2014, 11:59 AM
    I have to say, even though I know this will be an unpopular opinion, if you do not know the difference between a 1-pole and a 2-pole breaker, and you are considering #8 cable for a 50A circuit, you will be best served hiring an electrician to do this job.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #4

    Oct 10, 2014, 06:17 PM
    Amen.
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #5

    Oct 11, 2014, 06:15 AM
    Amen x2
    davidloi's Avatar
    davidloi Posts: 2, Reputation: 1
    New Member
     
    #6

    Oct 13, 2014, 07:30 AM
    Thanks HKSTROUD for confirming for me which breaker and wire to buy and everyone else for your input. I do intend to hire a licensed electrician to hook everything up so it doesn't go poof! Amen (x2) indeed if I don't *LOL*
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #7

    Oct 13, 2014, 10:03 AM
    Let electrician purchase cable and breaker. Specifications of water heater calls for #8 cable but there are different types of cable. If distance is very much it may be best to use aluminum cable.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How to change a 20 amp single pole to a ge 45 amp circuit breaker one pole? [ 5 Answers ]

I have a 20 amp service in my garage and I want to plug in my camper. The camper has an inverter that says it is rated for 45 amps. I changed the breaker to a 30 amp but it keeps popping the GFI outlet. How do I convert this amperage to meet the needs of the camper?

Why is only one breaker on a two pole circuit working [ 8 Answers ]

I have a sub panel run from a 60 amp breaker on the main panel. I installed a new double pole 30 amp (two 30 amp breakers joined together) in the sub panel but only one of the breakers seems to be working according to my tester. I noticed that another breaker, a 20 amp single pole circuit...

How Double Pole Circuit Breaker Trip? [ 9 Answers ]

On my electrical service panel, the "MAIN" breaker is a double pole breaker and each side is marked "100 Amps." Does that mean that when the total amperage exceed 100 one side it will trip, or if the total of both sides exceed 100 amps it will trip? Also, I recently bought a new electric range. I...

Difference between one pole and two pole circuit breakers. [ 1 Answers ]

Please explain in detail the difference between one pole and two pole circuit breakers. Thank you.

One pole of untied double-pole circuit breaker breaks [ 5 Answers ]

I recently purchased a new dryer (220 v appliance) to replace an older model. The old dryer was connected to the panel via a double-pole breaker except that there was no clip or tie between the poles. I changed the location of the outlet when installing the new dryer, replacing the cable with the...


View more questions Search