Why is only one breaker on a two pole circuit working
I have a sub panel run from a 60 amp breaker on the main panel. I installed a new double pole 30 amp (two 30 amp breakers joined together) in the sub panel but only one of the breakers seems to be working according to my tester. I noticed that another breaker, a 20 amp single pole circuit breaker, is also not working. What's happening?
Thanks, jp
|
|
 |
Home Improvement & Construction Expert
|
|
Apr 14, 2010, 10:31 AM
|
|
60 amp breaker on the main panel
Is that a double pole breaker?
|
|
 |
New Member
|
|
Apr 14, 2010, 10:33 AM
|
|
Yes, the 30 amp is a double pole breaker that is handle tied.
|
|
 |
Home Improvement & Construction Expert
|
|
Apr 14, 2010, 10:36 AM
|
|
The question was " Is the 60 amp breaker in the main panel a double pole"?
|
|
 |
New Member
|
|
Apr 14, 2010, 11:34 AM
|
|
Yes, the 60 amp breaker is double pole as well.
|
|
 |
Printers & Electronics Expert
|
|
Apr 14, 2010, 11:58 AM
|
|
Sounds like you lost one leg of Phase.
How did you wire up the 60 amp breaker?
Did you use 4 conductor feed to the sub?
Do you have a multi meter? If so, tell me the voltage you see coming out of each breaker connection between Neutral and each Breaker. Also, tell me what is the voltage when connected to only the Breaker Out connections/
Can you append a picture for us to see the wring in both the main panel and sub panel, please?
|
|
 |
Home Improvement & Construction Expert
|
|
Apr 15, 2010, 04:35 AM
|
|
Yes, can you show us a picture? The last time someone told us they were using a double breaker, the picture showed two separate breakers on the same leg.
|
|
 |
New Member
|
|
Apr 15, 2010, 06:37 AM
|
|
Don and Harold, I had all good intentions of posting a pic after I got home last night when something one of you said clicked in my head. I checked the feed and noticed that one of the hot wires was severed in a junction box. Side note, the other was frayed pretty bad so it was kind of a blessing to find it so it could be fixed. Long story short, I ran a new 8/3 (bigger than I needed... but will save me some trouble if I grow the sub panels capacity in the future) and got everything working like it should.
Thank you both for the help... I wish it would have occurred to me initially that there was a problem with one of the hot wires in the feed if only half of my bus bar was working. Thanks again.
|
|
 |
Home Improvement & Construction Expert
|
|
Apr 15, 2010, 07:48 AM
|
|
What type of cable you using? 8/3 will not carry 60 amps. Switch 30 and 60 breakers. 60 amp breaker will then be a just a disconnect.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
A/C circuit breaker tripped but working now.need to diagnose.
[ 28 Answers ]
My A/C circuit breaker tripped two nights ago (after a huge rain shower in the evening), and each time I reset it, it tripped within 3 seconds. I then, shut OFF the Main, reset the A/C circuit breaker, and then turned ON the Main. The A/C has been working fine ever since. What do you think was the...
Using Double pole circuit breaker for two separate circuits
[ 2 Answers ]
I am wiring my basement with 3 circuits for about 24 receptacles. We used to have electric baseboard heat and the 20 Amp Double pole breakers from the heaters are still there but disconnected. Can I use each double pole breaker for two separate circuits? Can I use one leg of another double pole...
How Double Pole Circuit Breaker Trip?
[ 9 Answers ]
On my electrical service panel, the "MAIN" breaker is a double pole breaker and each side is marked "100 Amps." Does that mean that when the total amperage exceed 100 one side it will trip, or if the total of both sides exceed 100 amps it will trip? Also, I recently bought a new electric range. I...
One pole of untied double-pole circuit breaker breaks
[ 5 Answers ]
I recently purchased a new dryer (220 v appliance) to replace an older model. The old dryer was connected to the panel via a double-pole breaker except that there was no clip or tie between the poles. I changed the location of the outlet when installing the new dryer, replacing the cable with the...
View more questions
Search
|