    I am installing 200amp service 450 feet underground will 250 urd be enough.
    200 amp service 450 feet underground will 250 urd cable be enough.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Oct 3, 2014, 07:21 AM
    If you truly need 200 amp, then you will need 350 kcmil conductors for 450 ft. That will give you just under 3% voltage drop leaving you an additional 2% end to end recommended max of 5% voltage drop.

    Also, if this from a main service panelboard to a downstream panelboard, then you must use a four wire feed to the downstream panelboard and an independent grounding and bonding system must be set up at the secondary site.


    Neutral from the main service panelboard must be isolated from the grounding system at the secondary panelboard.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Converting 200amp.service to extra box ,100amp. back to 200amp.service [ 2 Answers ]

I have new 200 amp.service in my home;then I had a second box installed,and it is 100amp. and that also runs to my guest house,which is 100 amp.How do I change the first box to 20 amps. and then change the one in the 'guest house" to 200 amps.

100 amp service 450 feet from pole [ 3 Answers ]

100 amp service 450 feet from pole. 10 4 foot floresant light fixtures 80 watts ea. 4 3 speed fans watts? Guess 500? Kitchen area: 1 window AC unit guess 2400 watts 1 microwave unit guess 2000 watts 1 12 cup coffee maker 1200 watts 1 Rifrigerator 600 watts Bath...

Got a 200amp service can I run another two 50amp breaker in the 200amp service [ 0 Answers ]

I got a 200amp service put in and I'm trying to get a electric stove in the basement will that 200amp service be enough power for two stove or will I have to run a sub-panel

Charge for a project 12,450 square feet. [ 2 Answers ]

How to charge for project for a 12,450 square feet.

Wire sizing for 250 feet service [ 5 Answers ]

I'm running an underground electrical service (240 volt) from the meter to the house, 250 feet. What would the wire size be and the size of the conduit? The main panel will be 200 amps. I would like to get a price for both aluminum and copper. Thanks


View more questions Search