    100 amp service 450 feet from pole
    100 amp service 450 feet from pole.

    10 4 foot floresant light fixtures 80 watts ea.
    4 3 speed fans watts? Guess 500?
    Kitchen area:
    1 window AC unit guess 2400 watts
    1 microwave unit guess 2000 watts
    1 12 cup coffee maker 1200 watts
    1 Rifrigerator 600 watts
    Bath Room:
    1 light/fan 400 watts

    Rounding up guestimate 10,000 watts or 84 amp.

    What size wire would you suggest for 120 voilts single phase service??
    mike 165278's Avatar
    mike 165278 Posts: 168, Reputation: 7
    Junior Member
     
    #2

    Dec 26, 2012, 07:08 PM
    Copper or aluminum conductors? Are you sleeving it in pipe, direct burying it, ariel? And that's a pretty far run explain your situation to us.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Dec 26, 2012, 07:26 PM
    120V? I think you mean 120/240V.

    Don't tell me that for one second you were considering just 120V for such a job.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Dec 27, 2012, 05:30 AM
    I am sure the poster does not realize a standard residential service is 120/240 volts, or simply two 120 volt legs.

    The installation, based on the listed loads, sounds like a hunting cabin, or similar.

    I would suggest using #4/0 aluminum wire, using a 4 wire direct burial cable called URD. This can be buried directly in ground, using 6 inches of sand below and above. Being such a long distance, for additional protection, I would suggest using 4 inch Sch40 PVC conduit as a sleeve.

    You will need to splice #2 wire onto the #4/0 to reduce the wire size at the panelboard, as the lugs will not accept the #4/0 wire.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Sub-panels with 50 amp outlet and breakers being fed by two pole 100 amp main service [ 3 Answers ]

I have a number of sub-panels with a 50 amp breaker for a 50 amp RV outlet being fed by a two pole 100 amp main service 120/240, I want to know how many 50 amp outlets I can safely install, will I need to upgrade the main service panel to accommodate more 50 amp RV outlets?

100 amp main, 100 amp service wire, 200 amp sub panel? [ 2 Answers ]

I am moving my sub panel and upgrading to a 200 amp service, but in phases. The first phase is to move the panel due to some remodeling. I want to put a 200 amp panel in the laundry room with a 200 amp breaker. I have 100 amp feeder wire going to it (AL 2/2/2). Outside I have the meter can and...

What size wire for 220v 100 amp service at 100 feet [ 7 Answers ]

I am running 220v 100 ft to a 125 amp sub panel. A welder would be the heaviest thing used. (around 200 amp welder) what size copper wire would I need running in pvc underground

100 amp service to my pole barn [ 1 Answers ]

I am installing a 100 amp service in my pole barn. It is 250 feet from the house panel. What size wire and conduit do I need to bury for that distance? Thank you

Service entrance cable (alum) size for a 100 amp service at 186 feet for a garage [ 1 Answers ]

The garage is 186' from the service at the house. I wanted to make sure the voltage drop would not cause a problem.


View more questions Search