    AC Fan starts then stops
    My AC fan stopped working a few days ago. I have checked a number of things and replaced the capacitor and contactor. The fan still didn't run. I then replaced the fan motor and the fan now starts and runs but shuts off after a minute or so. The compressor is running and I have checked that the unit is getting 240v. What else could I check?
    bitters's Avatar
    bitters Posts: 348, Reputation: 12
    Full Member
     
    #2

    Aug 20, 2014, 09:23 AM
    I suspect the capacitor might be wired wrong. Is the new motor a 3 wire or 4 wire? Fan model number would help.
    ttx3's Avatar
    ttx3 Posts: 5, Reputation: 1
    New Member
     
    #3

    Aug 20, 2014, 09:36 AM
    Thank you for responding.It is 4 wires. The old motor was 3. 2 are going to the 'fan' on the capacitor and the other 2 are going to the contactor. The fan starts and runs in high speed but turns back off after 1 minute or so. I let it cool down and tried it again with the same behavior.
    bitters's Avatar
    bitters Posts: 348, Reputation: 12
    Full Member
     
    #4

    Aug 20, 2014, 10:04 AM
    Ok, when you go from a 3 wire to 4 wire motor, you need to use a separate single cap. It sounds like you using the duel cap. Look on the cap and find the mfd, it should look like 35/5. You will want to use the smaller number, to get a new cap.
    ttx3's Avatar
    ttx3 Posts: 5, Reputation: 1
    New Member
     
    #5

    Aug 20, 2014, 10:12 AM
    Is a new single cap the only option? I thought I could use the duel cap. Not a problem to pick up a single cap.

    Model number of the fan is S1-FHM3729. Dual cap is 55uf/7.5uf
    bitters's Avatar
    bitters Posts: 348, Reputation: 12
    Full Member
     
    #6

    Aug 20, 2014, 10:22 AM
    Yes that is your only option, with the duel cap the motor is tripping off on overload. The bottom diagram shows how you want to wire it. Let me know how it turns out. Ok, 7.5 is what you need.

    Name:  fan motor 3 and 4 wire.png
Views: 35
Size:  287.1 KB
    ttx3's Avatar
    ttx3 Posts: 5, Reputation: 1
    New Member
     
    #7

    Aug 20, 2014, 11:22 AM
    Thank you very much. I will get this done tonight and let you know. The diagram helps a ton. Another person told me I could connect one to the 'fan' portion on the dual cap, the other to 'c' on the dual cap, and only connect one wire to the contactor. The remaining wire could be capped and not used.
    ttx3's Avatar
    ttx3 Posts: 5, Reputation: 1
    New Member
     
    #8

    Aug 21, 2014, 07:25 AM
    Well, as luck would turn out, I didn't make it in time to pick up a new single run contactor. I did get the fan to work. Turns out, 2 of the four wires are actually the same. I connected only 1 to the dual run cap and the other 2 to the contactor. I 'capped' the remaining wire and everything the fan runs great. I think I could have also connected that remaining wire to the 'c' terminal on the dual run cap. Would have had the same effect I think.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

My furnace fan starts, then stops [ 3 Answers ]

I put a new blower motor in my furnace the blower comes on the stop what can I do too get to work Thank you

Payne 394gaw furnace - main gas starts/stops/starts/stops [ 0 Answers ]

I have a Payne 394gaw furnace. The house thermostat calls for heat, the igniter assembly sparks and lights fine. (problem 1): It takes about three minutes for the thermocouple in the igniter assembly to close (problem 2): The main gas starts, runs for about 10 seconds, then stops, then...

Fan motor starts for a second then stops [ 0 Answers ]

Goodman heat pump, fan motor starts for a second then stops about 10 seconds it tries again.

Goodman furnace problems when running the ac it starts stops starts stops [ 1 Answers ]

I have a goodman furnace 98% efficient it works fine on heat but when I run the ac unit it will run fine for an hour or three but then it will start stoping and starting the blower motor I have changed the transformer the blower motor the door switch anyone have any idea why it does this any help...

Condenser Fan stops and starts [ 1 Answers ]

I have a Bryant system and I have replaced the cap and the fan motor on the outside unit. My question is this, should the condenser fan always run when the pump is on or does it regulate the temperature and turn the fan on as needed. I thought it ran constantly as long as the unit was on. ...


View more questions Search