    Wire gauge
    Hello:
    Is there any problem with using a larger gauge wire, say 8, for an electric water heater on a dual pole 30amp breaker? That wire is already run and I didn't want to run a new one.
    Thanks.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Apr 11, 2014, 09:14 AM
    First, how do you know the cable is an 8 AWG cable? Did you look at the cable, it should be marked with its size on the sheath.

    Now to answer your question, no, there are no problems using a larger cable gauge as long as the connections are made properly.
    Needshelp17's Avatar
    Needshelp17 Posts: 18, Reputation: 1
    New Member
     
    #3

    Apr 11, 2014, 09:15 AM
    Quote Originally Posted by donf View Post
    First, how do you know the cable is an 8 AWG cable? Did you look at the cable, it should be marked with its size on the sheath.

    Now to answer your question, no, there are no problems using a larger cable gauge as long as the connections are made properly.
    Thanks Don, the sheath has it marked as 8.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #4

    Apr 11, 2014, 01:21 PM
    Any larger wire can be used. Make sure they are the same class and temp rating.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Is it safe to replacing a lighter gauge wire with a heavier gauge [ 11 Answers ]

Hi all, One of my baseboard heater (240v)'s wire was broken can I replace it with a heavier gauge wire? Also can different gauge ground wires (copper wire) be connected with a wire-nut? IS THIS SAFE TO DO? OR Will this create a fire hazard?

Can I connect 14 gauge wire to a light fixture that came with 16 gauge wire [ 4 Answers ]

Can I connect 14 gauge wire to a light fixture that came with 16 gauge wire. This is for lighting in a outside shed.

Can I connect 12 gauge wire to 10 gauge wire [ 2 Answers ]

I had an existing 30A breaker with 10-3 wire. I capped the red wire on both ends and replaced the 30A breaker with a 20A beaker. At the end of the run (nothing else is tied to this wire/breaker), I want to connect 12-2 wire. Is there anything wrong with doing this? I understand that it is not best...

I ran 6 gauge wire from my breaker then connected to 10 gauge to my hot tub [ 1 Answers ]

I had a hot tub that ran with 10 gage wire. I bought a new one and was told Run 6 Gage from breaker to a sub panel. I was told I could use my 10 Gage Wire I already have in place. Is this true

Connecting 14 gauge wire and 12 gauge wires in the same blue box. [ 2 Answers ]

I am wiring my basement. All the outlets are running off 2 independent 20 amp circuit breakers connected to each other by 12/2 wire. I wanted to run some stubs off my 12/2 outlets. All each stub would do is run to a small light (max 180 watts) and of course a light switch. Since I ran out...


View more questions Search