    Can I connect 12 gauge wire to 10 gauge wire
    I had an existing 30A breaker with 10-3 wire. I capped the red wire on both ends and replaced the 30A breaker with a 20A beaker. At the end of the run (nothing else is tied to this wire/breaker), I want to connect 12-2 wire. Is there anything wrong with doing this? I understand that it is not best practice, but is there anything unsafe or against code
    With this scenario?
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #2

    Apr 7, 2012, 09:35 AM
    Paoke,
    Acutally you are permitted to connect #12 AWG conductors "and Larger" to a 20 ampere circuit breaker.
    This is done frequently to reduce voltage drop across large distances, so it's not only a permitted practice but a common one, assuming of course the rest of your work is code compliant!
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Apr 8, 2012, 04:10 AM
    Yes, you can extend the circuit with #12 wire and protect it with a 20 amp breaker. Be sure to label the #10 wire in the panel to warn that there is #12 wire in the circuit and the max breaker allowed to protect that circuit is 20 amp.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Is it safe to replacing a lighter gauge wire with a heavier gauge [ 11 Answers ]

Hi all, One of my baseboard heater (240v)'s wire was broken can I replace it with a heavier gauge wire? Also can different gauge ground wires (copper wire) be connected with a wire-nut? IS THIS SAFE TO DO? OR Will this create a fire hazard?

I ran 6 gauge wire from my breaker then connected to 10 gauge to my hot tub [ 1 Answers ]

I had a hot tub that ran with 10 gage wire. I bought a new one and was told Run 6 Gage from breaker to a sub panel. I was told I could use my 10 Gage Wire I already have in place. Is this true

Can I connect a 10 gauge wire to a 12 gauge wire [ 5 Answers ]

I have 20 amp circuit with 12/3 wire and want to attach 10/3 wire to it. Can't this be done?

Connecting 14 gauge wire and 12 gauge wires in the same blue box. [ 2 Answers ]

I am wiring my basement. All the outlets are running off 2 independent 20 amp circuit breakers connected to each other by 12/2 wire. I wanted to run some stubs off my 12/2 outlets. All each stub would do is run to a small light (max 180 watts) and of course a light switch. Since I ran out...


View more questions Search