    I am connecting to a 200 amp service panel and 300' to a 100 amp sub panel. #4 or #2
    I am connecting to a 200 amp service panel and running 300 ft to a 100 amp sub panel. At the 100 amp sub panel it will be running mostly lights and a occasional small appliance. Do I need to use #2 for the hot leads or can I get by with #4 ?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Apr 10, 2014, 11:25 AM
    Before you start trenching, can your main service panel accept a 100 breaker?

    Next issue, if go from the main service panel to a downstream panelboard, you must use a 4 wire feed.

    Next, to deliver 240 volts - 100 amps a distance of 300' will require 2/0 AWG copper conductors. For Aluminum, you would need 4/0 conductors.

    That's allowing for a 3% Voltage drop. The recommended allowance is 5% end to end (feeder and branch circuit).
    ixoye55's Avatar
    ixoye55 Posts: 2, Reputation: 1
    New Member
     
    #3

    Apr 11, 2014, 05:58 AM
    Quote Originally Posted by donf View Post
    Before you start trenching, can your main service panel accept a 100 breaker?

    Next issue, if go from the main service panel to a downstream panelboard, you must use a 4 wire feed.

    Next, to deliver 240 volts - 100 amps a distance of 300' will require 2/0 AWG copper conductors. For Aluminum, you would need 4/0 conductors.

    That's allowing for a 3% Voltage drop. The recommended allowance is 5% end to end (feeder and branch circuit).
    Thanks

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Updating service panel to 200 amp with feeder to 100 amp panel in old house [ 8 Answers ]

I currently in the process of converting 1000 sq ft of attached garage into living space while doing this we are updating electrical service to 200 amp new service, there is 100 amp service in the old part of the house which will remain but need to be sub paneled from the new 200 amp service. I...

100 amp main, 100 amp service wire, 200 amp sub panel? [ 2 Answers ]

I am moving my sub panel and upgrading to a 200 amp service, but in phases. The first phase is to move the panel due to some remodeling. I want to put a 200 amp panel in the laundry room with a 200 amp breaker. I have 100 amp feeder wire going to it (AL 2/2/2). Outside I have the meter can and...

125 amp service panel tapped from the line side of my 200 amp service panel. [ 1 Answers ]

I have a 125 amp service panel for my basement, being fed from the line side of my 200 amp service panel. Is this legal? Does the 10 foot tap rule apply here?

I need help determining ihelp new 100 amp service panel or upgrade to a 200 amp [ 12 Answers ]

I've gotten conflicting advice from different electricians. We have a 40 year-old house with original 100 amp panel. It's about 1800 sf. I think we have the usual demands for a family of 4, 2 tv's, stereo, 3 laptops, printer, washer, dishwasher, plus a pool pump and filter (no heat or spa), etc....

Using 100 amp panel on 200 amp service [ 5 Answers ]

I am building new camp at a site that already has 200 amp service. My power requirements are small and 100 amp will be more than sufficient. Is there any reason I cannot hookup a 100 amp panel to the 200 amp meter socket? Not sure is code allows this. I want to use a small 100 amp panel vs the...


View more questions Search